February 26, 2009 Update - Lubrizol is providing this update regarding the use of antimicrobial coated steel pipe with BlazeMaster(r) CPVC fire sprinkler piping systems. Contractors should not use steel pipe with antimicrobial coatings, such as Allied's ABF II, in conjunction with BlazeMaster CPVC pipes and fittings, unless the factory applied coated steel pipe has been approved for inclusion in our FGG/BM/CZ(tm) System Compatible program (www.systemcompatible.com). This recommendation covers antimicrobial coatings that are applied by the pipe manufacturer or sold separately in the aftermarket. At this time, Wheatland Tube Company's MIC SHIELD(tm) Coating (for steel pipe manufactured after 2/22/2009-the date when the product's validation was completed) is part of the FGG/BM/CZ System Compatible Program. For Wheatland Tube MIC SHIELD(tm) coated pipe manufactured before 2/22/2009 please contact Wheatland Tube for clarification. In the aftermarket, Potter Pipe-Shield(tm) corrosion inhibiting antimicrobial liquid is approved as part of the FGG/BM/CZ System Compatible Program. The coating must be applied and used in accordance with the manufacturer's installation instructions.
Top Myers RelMark Group 961 Pottstown Pike Chester Springs, PA 19425 Office 610-321-2415 Cell 610-952-0965 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, April 01, 2009 8:31 AM To: [email protected] Subject: RE: CPVC I was in error in my previous post. The list was generated by Lubrizol. Here is the web site: http://www.systemcompatible.com/products-americas.asp. I confess I haven't explored it in great detail yet, but that may have some good information At 08:31 AM 4/1/2009, you wrote: >We had a BlazeMaster Rep in the office last year and he did cite >cases where the CPVC failed prematurely due to threading compounds >and a few other materials. They have some information on >compatibility of chemicals with their systems. I would suggest you >tell your friend to contact the mfgr. of the pipe he's using for >specific information on compatibility issues. > > >Craig L. Prahl, CET >Fire Protection Specialist >Mechanical Department >CH2MHILL >Lockwood Greene >1500 International Drive >PO Box 491, Spartanburg, SC 29304-0491 >Direct - 864.599.4102 >Fax - 864.599.8439 >[email protected] >http://www.ch2m.com > > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Chappell, Carl >Sent: Tuesday, March 31, 2009 7:58 PM >To: [email protected] >Subject: FW: CPVC > >Does anyone have any information regarding the request >below? Thanks in advance. > > > > > >Carl Chappell > > > >________________________________ > >From: Chris Brown [mailto:[email protected]] >Sent: Tuesday, March 31, 2009 3:45 PM >To: Chappell, Carl >Subject: CPVC > > > >Carl, > > > >Can you ask the sprinkler forum if anyone has read a case study >regarding the compounds (oils for protection) used inside steal pipe >not being compatible with CPVC? > > > >Thank you, > > > >Chris Brown >Managing Partner > > > >Certified Life Safety, LLC >5880 West 319th Street >Louisburg, Kansas 66053 >Telephone: 913.636.2260 >Fax: 913.837.4195 >Toll Free: 877.707.FIRE (3473) >Web: www.certifiedlifesafety.com > > > >Email Confidentiality Statement: This message and accompanying >documents are covered by the Electronic Communications Privacy Act, 18 U.S.C. >2510-2521, and contains information intended for the specified >individual(s) only. This information is confidential. If you are >not the intended recipient or an agent responsible for delivering it >to the intended recipient, you are hereby notified that you have >received this document in error and that any review, dissemination, >copying, or the taking of any action based on the contents of this >information is strictly prohibited. If you have received this >communication in error, please notify us immediately by E-mail, and >delete the original message. > >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)