So if I read this right, we have to extend the hydraulic criteria 15 
ft beyond the hazard and the higher temperature sprinklers 30 ft 
beyond? We are using 2002 in this jurisdiction, so that section 
doesn't apply (yet), since it is new. I may just do the whole thing 
in 286 and see what they say. Of course, it will probably be 
installed, tested and in service before the engineer completes his 
review, give what's been going on lately.


At 09:09 AM 4/23/2009, you wrote:
>Todd, check out Table A.12.3 in the '07.  I sounds like it may apply.
>
>
>Jimmy Waite
>Burtell Fire Protection
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Thursday, April 23, 2009 5:58 AM
>To: [email protected]
>Subject: RE: 286 & 155
>
>Open to structure, 16-18 ft high, no ceilings.
>
>
>At 07:55 AM 4/23/2009, you wrote:
> >Ceilings, heights?
> >
> >
> >
> >I am working on a job where there is a storage area that is open (no
> >separation) to a retail space. The spec calls for 286 sprinklers over
> >the storage, plus 15 ft beyond and 155 degree over the retail area.
> >This would result in 4 lines with 286 and 8 with 155. This can be
> >done easily on paper, but is it practical in reality?
> >
> >Todd G. Williams, PE
> >_______________________________________________
> >Sprinklerforum mailing list
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to