I am working on a large wood-frame building with a LH occupancy. They 
are running ductwork down from the attic along the columns on the 
second floor to feed the first floor HVAC. They oversized some of the 
chases (4' x 1.5' and 6' x 1.5') for architectural reasons. The chase 
walls are sheetrock on wood stud. The top of these was going to be 
open to the attic, so I assumed that the sprinklers in the attic 
would provide any needed protection to those areas. Now the AHJ is 
making them cop the chases for smoke control reasons. Therefore, we 
now have combustible shafts with no protection. According to 8.14.2 
(NFPA 13 - 2002), these would need to be sprinklered. As an 
alternative, could the shaft be filled with insulation similar to 
8.14.1.2.7? This is going to add a bunch of sprinklers into 
non-accessible spaces, which I would like to avoid.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  