TY3334 R3531 VK442 Listings are from 4-12" or 6-12" check each data sheet. Not aware of any that are 1-12"
Bryan A. Dann Dannba Design Services, LLC Fire Sprinkler Designs Office: (740) 363-5878 Cell: (740) 803-0967 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Rod DiBona Sent: Friday, May 01, 2009 1:28 PM To: [email protected] Subject: sidewall heads I had it in my mind that there is or used to be a sidewall that was listed from 1" - 12" below the ceiling. Maybe I am dreaming this up. We have a motel that is raising the ceiling in the corridor after heads have been installed. The heads we have installed are listed at 4"-6" below ceiling. Does anyone remember if there was such an animal and does it still exist? Thanks. <http://www.rapidfireinc.com/> Rod DiBona Vice President 605-348-2342 office 605-348-0108 fax 605-391-3553 cell _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)