Logic? NFPA 13? Considering the exception to section 11.2.3.1.8 (3) 
only encompass 5 of the 14 situations described in 8.14.1.2, my guess 
would be that the 3000 sqft requirement would apply.



At 10:09 PM 5/7/2009, you wrote:
>No takers for my original questions. So let me try again.
>
>16" deep TJI's (composite wood construction). Sprinklers can be upto 6"
>below the bottom of the TJI's and comply with NFPA for obstructed
>construction. Same scenario, but with drywall or insulation at the bottom of
>the TJI's forming an unsprinklered combustible space. Does it trigger the
>3000 sq.ft. design? If it does, I fail to see the logic.
>
>Tony
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of A.P.Silva
>Sent: May 5, 2009 2:41 PM
>To: [email protected]
>Subject: Combustible crawlspace
>
>
>A crawlspace comprising of a wood deck, 16" deep TJI's and open space below
>the TJI's. Between the TJI's there is batt insulation, kept in place with
>wire mesh attached to the bottom flanges of the TJI's. The insulation is
>only couple of inches (approx) thick and doesn't fill the entire TJI space.
>The crawlspace is 1 foot deep at the perimeter and 4 feet at the centre of
>the building. The depth is from bottom of the TJI's to the ground. The
>crawlspace is being sprinklered.
>
>Questions:
>
>(1) Are the pockets formed by the TJI's and insulation have to be
>sprinklered? If there was no insulation, the sprinklers could be below the
>bottom of the TJI's due to obstructed construction. The pockets are less
>than 160 cuft in volume, but there is no non-combustible or limited
>combustible ceiling at the bottom. Just non-combustible insulation and wire
>mesh. My opinion is the insulation can be ignored. The sprinklers will be at
>the permitted distance below the deck, so the pockets don't have to be
>sprinklered and the 3000 sq.ft. design is not required. Anyone disagree?
>
>(2) The height below the bottom of the TJI's vary from 1 foot to 4 feet. Are
>combustible concealed space sprinklers required? (using NFPA 13, 2007) I
>don't think it will be a good design to have them only at the perimeter and
>standard heads at the centre. Section 8.15.1.7 states that the listed
>sprinklers are "permitted" to be used to protect composite wood joist
>construction less than 36" "between the top of the bottom joists and bottom
>of the upper jpists". (In other words the depth of the TJI's. Could this be
>a mistake, as the TYCO cut sheets show this distance from the bottom of the
>TJI's to the ceiling). In anycase, it appears that the listed heads don't
>have to be used for composite wood joist construction, due to the use of the
>word "permitted". Anyone agree/disagree?
>
>Sub-questions:
>
>(3) If the construction was combustible wood truss or joists, the listed
>sprinklers may have to be used, depending on the height of the space. What
>happens when the height varies such as in my case?
>
>(4) NFPA imposes the requirement of cc sprinklers depending on the depth of
>the space. However, Tyco imposes other restrictions, such as maximum 54"
>from deck to deck for solid wood joist consruction. What happens if Tyco
>requirements are not met, and the listed heads are required by NFPA?
>
>Tony
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to