Note the following two "one-year maximum age" rules:

 

*       (2007) NFPA 14 10.2 provides a standpipe system water supply test 
procedure requirement that "Tests for the purpose of system design shall not be 
conducted more than 1 year prior to system design."

*        The South Carolina Fire Protection Sprinkler Systems Act 
[http://www.scstatehouse.gov/code/t40c010.htm 
<http://www.scstatehouse.gov/code/t40c010.htm> ], administered by the South 
Carolina Contractor's Licensing Board, provides a statutory maximum flow test 
age in ยง40-10-250(A)(1): 

SECTION 40-10-250. Fire Protection Sprinkler System Specification Sheet; 
completion of form; attachment to building permit applications. 

(A) A "Fire Protection Sprinkler System Specification Sheet" must be completed 
for every fire protection sprinkler system, and submitted on a form approved by 
the State Fire Marshal's Office to the authority having jurisdiction. The 
completed form must contain the following information at a minimum: 

(1) the available static and residual water pressure from a flow test conducted 
less than one year before submittal; 

(2) the volume per minute of the available water flow and duration; 

(3) the source of water supply; 

(4) the NFPA hazard classifications and details of storage arrangement, if 
applicable; 

(5) the occupancy use of the building, or the area to be sprinkled; 

(6) the type of system to be installed; 

(7) the applicable National Fire Protection Association standards to be 
followed for each component of the system; 

(8) other state and local statutes, regulations, codes, or ordinances that must 
be followed; 

(9) the name, address, title, and phone number of the person developing the 
fire sprinkler system specification sheet. 

(B) The form must be completed by: 

(1) a professional engineer licensed in this State bearing his professional 
seal and signature; or 

(2) a fire sprinkler contractor licensed in this State with a qualifying party 
holding a NICET Level IV Technician Certification in "Fire Protection 
Engineering Technology Automatic Sprinkler System Layout" if a specific 
statute, regulation, or ordinance does not require the services of a licensed 
professional engineer. The qualifying party must be the individual completing 
the form, and he must place his name on the lower right hand corner on the 
first page of the form with the words "Qualifying Party" after his name and 
with his qualifying party certificate number. 

(C) When applying for building permits or other required permits, the Fire 
Sprinkler System Specification Sheet completed in accordance with subsections 
(A) and (B) must be made part of the bid documents and must be submitted to the 
authority having jurisdiction, along with the architectural or engineering, or 
both, drawings and specifications. The completed Fire Sprinkler System 
Specification Sheet must accompany the shop drawings when they are submitted 
for review. 

We deem one year a reasonable general maximum; however, the designer is 
ultimately responsible for determining the adequacy of the water supply.  The 
commentary to (2007) NFPA 13 23.1.2 in the Automatic Sprinkler Systems Handbook 
details the necessary considerations regarding the designers evaluation of the 
adequacy of the water supply capacity and emphasizes its critical importance:  
"It is important to note that, regardless of how well the sprinkler system was 
designed and installed, if the water supply fails, the sprinkler system will 
fail."

 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
<http://www.llr.state.sc.us/firemarshal.asp>  
---------------------------------------------------------------- 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to