Phil,

There are some rules that allow the "decking" to be measured from the
bottom of non or limited combustible materials such in steel buildings
where you have the exposed insulation visible between rafters. I can't
recall if there's some caveat about the structural materials needing
to not be combustible, and don't have any books at home so I can't
look anything up, but trying fishing in that type of pond.

On Sat, May 16, 2009 at 6:13 AM, Phil Nawrocki <[email protected]> wrote:
>  Sirs,
>
> We have a contract to install fire sprinklers in a building with 24" deep
> TJI composite wood joist construction.  They are 24" on center.  I can find
> nothing in NFPA #13 deflector rules that allow the sprinkler deflector under
> obstructed construction to be below 22" from the deck.  Is there any other
> way to protect the area besides putting a sprinkler in each 24" wide joist
> space?
>
> Regards,
>
> Phillip H. Nawrocki
> Design Manager
> National Fire Sprinkler, Inc.
> 1544 W. Grant St.
> Phoenix, AZ 85007-3314
> (602) 712-1180 Phone  Ext #33
> (602) 712-1260 Fax
> [email protected]
> Fire Sprinklers Save Lives!
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to