An excerpt from the email: "As a result of a false fire alarm, which occurred at approx 4:00am EDT, the preaction sprinkler system was triggered. A pinhole leak occurred while the sprinkler system pipes filled with water. The water leaked from the pipe, within the ceiling, from approx 4:00-6:00am, at which point a ceiling tile collapsed and water leaked into the datacenter. Four CAD locations <snip> were located beneath the leak. Water leaked onto the top piece of equipment in <SNIP>"
So yes, the leak was a pinhole in the sprinkler piping. No idea if SI or DI. No idea what caused the false trip. Don't know if there was a clean agent system in place that should have reacted to false trip faster and outen the fire so the PA system would have known it didn't need to false trip, the clan agent already did :) Understand my contact is managing servers, not piping, so I doubt I'll find out much more. If I do, I'll relay. glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Chris Cahill Sent: Monday, May 18, 2009 1:10 PM To: [email protected] Subject: RE: Fire Service College Fire: All 11 appliances lost I'm confused. Where was the leak? The sprinkler piping? Where was the monitoring air all this time? How does one false alarm a PA system? Or another way to put it is why do a single interlock and rely on fire alarms which in my experience are prone to false alarming? The 30% of DIPA isn't really that much of a cost? Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Church Sent: Monday, May 18, 2009 12:03 PM To: [email protected] Subject: RE: Fire Service College Fire: All 11 appliances lost So if not that tall building, and not the rural homes in PA where there's not much point in telling the FD to hurry since the home is ash and there is no water damage since the fire service in this town advised not to sprinkler, than are we back to just sprinklering the clean and dirty linen in non-high-rise nursing homes like the good old days? BTW, a relative reports a data center Preaction system tripped due to a false alarm, and of all things, a pinhole leak allowed water to accumulate above the ceiling, then it dropped and water entered two servers worth >$100k each. Best-laid plans of PEs and Risk Managers...... glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Monday, May 18, 2009 12:47 PM To: [email protected] Subject: RE: Fire Service College Fire: All 11 appliances lost Correction: His comments were in the context of defending an HOA (luxury seniors-only community) that was fighting a proposed high-rise ordinance that would have required sprinklers to be retrofitted to their building. He said that sprinklers are great, but that this isn't the best application for them. Imagine that, a 13 TC member going on TV to say that tall buildings filled with old people aren't the best application for residential sprinklers. Unbeevable. Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of ParsleyConsulting Sent: Monday, May 18, 2009 9:41 AM To: [email protected] Subject: Re: Fire Service College Fire: All 11 appliances lost You're making that up, he really didn't say that. I've warned you about that over-active imagination of yours in the past, George. Reminds me of something Steve Leyton and I heard said out here in San Diego, where a member of the NFPA-13 committee said on a news report that he didn't think sprinklers in a residential high rise would have any value. And no, I'm not making that up. -- PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [email protected] <mailto:[email protected]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website George Church wrote: > But if you'd had sprinklers when the ambulance burned, you'd have had > to not > only re-carpet, and likely a lot more of it, but also the bottom couple > inches of drywall would likely have needed replacement as well. > > Understand during the PA IRC hearings, a home builder who's a rural fire > chief noted that since it takes them 15 to 20 minutes to get to a fire, > sprinklers activated would continue to spray water on the > assumably-suppressed fire, causing water damage! Sure, delayed FD response > and resultant excessive water damage would be top of my list of why > I'd let > my house burn down instead of risking having to dry things out..... almost > went home and shut mine off right after the hearings..... > > glc > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Chris > Cahill > Sent: Monday, May 18, 2009 10:28 AM > To: [email protected] > Subject: RE: Fire Service College Fire: All 11 appliances lost > > Had this happen to my station once. Ambulance burned. The only reason we > didn't lose more than that was 1. The cable guy working out front noticed > the smoke in the early stages and 2. It was a after a drill and one of the > fire trucks was fully staffed at the local Perkins ~ 1 mile away. Had they > not been there probably would have been another 10 minutes waiting for > help > from our friends. Ambulance was a total loss, had to repaint the entire > building and re-carpet but not much more. > > Unfortunately, these things are far more common than you know. Food on > stove is common enough in paid houses 'cuz they run out for a call and > forget to turn the stove off. I can think of fire stations in MN that have > a fire every couple years. We're not a big place. And I'm sure I don't > know the half of it. > > Chris Cahill, P.E. > Fire Protection Engineer > Sentry Fire Protection, Inc. > > 763-658-4483 > 763-658-4921 fax > > Email: [email protected] > > Mail: P.O. Box 69 > Waverly, MN 55390 > > Location: 4439 Hwy 12 SW > Waverly, MN 55390 > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Stewart > Kidd > Sent: Saturday, May 16, 2009 5:55 PM > To: [email protected] > Subject: Fire Service College Fire: All 11 appliances lost > > Colleagues > > For once, I find myself a loss for words and I'm n sure whether to > laugh or cry ! > > The FSC is government-owned and is the UK's principle fire training > centre. The fire destroyed (I am told) all of the colleges fire trucks. > > Stewart > > http://news.bbc.co.uk/1/hi/england/gloucestershire/8053733.stm > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4083 (20090518) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4083 (20090518) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)