Tom You will need to determine what level quality of air is required by your client. You noted that your client is in the biomedical field which could require Medical Air grade compressor and piping (oil-less type compressor for medical air, desiccant dryers and brazed copper pipe with brazing done while pipe is purged with oil free nitrogen gas) see NFPA 99 for additional info.
If biomed there will be a maximum level of debris permitted in the piping as allowed by the FDA. You will need to discuss needs with client. Regards Jim Jim Davidson Davidson Associates Fire Protection * Medical Gas * Code Consulting 302-994-9500 Fax:302-234-1781 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Tom Duross Sent: Tuesday, May 19, 2009 8:31 PM To: [email protected] Subject: Compressed Air Piping I'm looking to specify a central plant air system for a testing client to put on the street. I've come up with a size but to save pipe size, I'd like to run 80-100 PSI air through their facility. Should I specify seamless and malleable/di or copper brazed? PR at use points, 22 locations, 25 floors. The building is new. Biomedical use if that applies. Thanks. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)