Very rare that a school gym won't have an occupant load of 300. I was in our
middle school gym last week with 6 or 700 friends and families of the 8th
grade class, plus the students teachers, and administrators. Our gym is less
than 10,000 sf.(Oh and did I forget the 6th & 7th grade band was there too!)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Reed Roisum
Sent: Wednesday, June 17, 2009 1:50 PM
To: '[email protected]'
Subject: RE: Gymnasium

Ether,

I was referring to IBC occupancy classifications.  This would most likely be
an A-4 occupancy (assuming IBC).  A-4 occupancies require and automatic
sprinkler system if the fire area exceeds 12,000 sq. ft, the occupant load
is over 300, or the fire area is on a floor other than the level of exit
discharge.  You don't have any of these (although you didn't sound too sure)
so it doesn't appear that you would need a sprinkler system.  However, if
this is a school and if it is a Group E occupancy, then you need to install
sprinklers if the entire fire area is greater than 20,000 sq. ft.  So, we
still need more info. to determine if a sprinkler system is required.

Reed A. Roisum, CET
Fire Protection Technician

Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of ETHER BARLOW
Sent: Wednesday, June 17, 2009 2:36 PM
To: [email protected]
Subject: Re: Gymnasium

9900 sqft 02' NFPA13, Bleachers on one side, Ground Level, OH1? Probably
about 150 people.
On Wed, Jun 17, 2009 at 12:17 PM, Reed Roisum <[email protected]>wrote:

> Need more info...  What code applies?  What is the occupancy 
> classification?  Is there spectator seating?  What is the square footage?
>  Occupant load?  Is it on a the floor level of exit discharge?
>
> Reed A. Roisum, CET
> Fire Protection Technician
>
> Ulteig Engineers, Inc.
> 3350 38th Avenue South
> Fargo, ND 58104-7079
>
> Direct Number: 701.280.8580
> Mobile: 701.212.8810
> Main Office: 701.280.8500
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of ETHER BARLOW
> Sent: Wednesday, June 17, 2009 2:07 PM
> To: [email protected]
> Subject: Gymnasium
>
>  Are Sprinklers required in a Gymnasium with a deck height of 50 ft, 
> noncombustible construction?
>
> --
> My Thanks to You!
>
> Ether J. Barlow
> Cell 702-375-1228
>  _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>



--
My Thanks to You!

Ether J. Barlow
Cell 702-375-1228
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to