Yeah, got that but it's the reasoning (in writing) that I'm looking for.
Thanks though.

Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[email protected]

Hello Russell,

This is not the "reasoning" but is the code section from NFPA 13 2007

7.2.6.2.2 The air supply shall have the capacity capable of restoring normal
air pressure in the system within 30 minutes

7.32.6.2.3 The requirements of 7.2.6.2.2 shall not apply in refrigerated
spaces maintained below 5 (degrees) F where normal system air pressure
shall be permitted to be restored within 60 minutes.