For the pressure tank it is not based upon fill time, but overall air
delivery.

7.2.10.1 An air compressor capable of delivering not less than
16 ft3/min (0.45 m3/min) of free air for tanks of 7500 gal
(28.39 m3) total capacity, and not less than 20 ft3/min
(0.57 m3/min) for larger sizes, shall be provided.

7.2.10.2 The compressor shall be located in the tank house.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Russell
Sent: Friday, June 19, 2009 7:55 AM
To: AFSA
Subject: Pressure tanks

Is the 30 minute air fill time requirement for dry systems applicable to
pressure tanks supplying wet systems? In other words, would the air pressure
need to be re-established in the pressure tank within 30 minutes?

 

 

 