Is there something new here?  Quick read it's nothing new. Even the spec
section is old.

Actually it's not an alternate IMHO.  Meets the same test standard as other
traditional materials used for rated walls.  If the AHJ would allow
sheetrock for example based on a UL listing then they would also have to
accept WS heads.  Even further one could use them in an otherwise
unsprinklered building.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dave Phelan
Sent: Monday, June 22, 2009 3:55 PM
To: [email protected]
Subject: Window Sprinkler for Fire Rated Assemblies

http://www.icc-es.org/reports/pdf_files/ICC-ES/ESR-2397.pdf

 

I know we occasionally get on the topic of design and such for window
sprinklers for alternate design for interior fire rated assemblies so this
might be worth tucking away for future use.

 

The ICC Evaluation Service has released an approval and design document for
providing window sprinklers as an alternate to fire rated assemblies in the
IBC.

 

Best wishes all -

 

Dave P.

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to