Jeff,

I also see (now) where they re-worded the language in 2007 edition and
removed the "when branchlines are run parallel to trusses and bar joists"
text. 

Thanks for your response.

Best Regards,
Ken Holsopple
Rowe Sprinkler Systems, Inc.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jeff Hewitt
Sent: Thursday, June 25, 2009 2:08 PM
To: [email protected]
Subject: RE: ESFR Spacing NFPA 13 2002 vs. 2007

You are allowed to move up to 1-ft. to avoid obstructions to discharge,
either along branch lines, or between lines, but not both at the same time.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation