There's a lot of Preaction on coal conveyors. PWire detection usually.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard Carr
Sent: Friday, June 26, 2009 6:40 AM
To: [email protected]
Subject: RE: Conveyor Sprinklers

No, not all, I have done some coal conveyors with fixed spray but
depending on the product being carried on the conveyor you may just need
standard sprinklers, best to check with the underwriter.

Richard Carr, SET
Design Manager
Associated Sprinkler Co., LLC
336.373.3901 ext 217
[email protected]