Reference Professor Pat Brock's "Fire Protection Hydraulics and Water Supply 
Analysis" as an excellent text on performing
these tests.  

In general, I prefer not to use large orifices (e.g. steamer connections).  Any 
voids (air bubbles, etc.) and highly turbulent flow from those openings will be 
difficult to obtain an accurate velocity pressure reading from, regardless of 
the experience and skill of the inspector/tester.  An appropriate distance from 
the connection is necessary to obtain a good reading.  I have found it 
difficult to hand hold steady the pitot knife on large openings such as a 
steamer connection.  I recommend that these not be used when the data obtained 
is going to be used for design purposes.

In addition, the law of small numbers applies.  If the small velocity numbers 
you reported were indeed accurate (I suspect they are not) one would want to 
use a gauge on the pitot of appropriate scale.  Gauges generally are most 
accurate when the expected reading is in the middle of the scale.  A good 
inspector/tester should use an appropriate scale gauge.  If the 
inspector/tester really expected to see a velocity of 6, then a 0-12 (more 
likely, a 0-25, or 0-50) gauge would produce a more accurate reading versus a 
0-100 or worse, a 0-300 scale gauge.

(In fact, one reason to suspect the 4-6 velocity numbers you reported is that 
they were most likely read or interpreted from a gauge that had a 0-100 PSI 
scale.  Trying to read numbers at either end of the scale with erratic void 
filled flow is dubious, at best.)

I would recommend the test be repeated using the appropriate method in the 
Brock text and I would recommend the smaller butts be measured and used.

Byron
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard
Lindner
Sent: Tuesday, June 23, 2009 3:25 PM
To: sprinklerforum
Subject: Hydrant Flow test results
 
Have a question regarding hydrant flow tests.
 
We have received a report where the contractor flow a single 2 1/2"
outlet
and gave us static, residual, pitot and calculated flow.  He then
performed
another test using the 4 1/2" outlet on the hydrant, again giving us
values.
 
Plotting the graph, is there supposed to be a correlation between the
testing of the 2 1/2" versus the 4 1/2" or are they supposed to be used
separately.  For example, when graphing the 2 1/2" outlet, the 4 1/2"
outlet
info should be hitting this line or not??
 
Also, is a pitot reading of a range of 4 to say 8 on a 4 1/2" outlet
valid
data?
 
We're not sure how to use this info.
 
Richard