One preaction system control valve is allowed to serve no more than 1,000 
sprinklers. 

If you have 1,650 sprinklers then you would need at least two separate 
preaction systems.  Breaking this large of a building up into three or even 
four systems might be a very good idea.  You might also consider separating the 
system run-ins into the building so that all systems are not fed from one 
single source.  

Depending on how this building is arranged and its size, you may want to or 
have to consider more than two systems.  

NFPA 11.2.3.2.5 doesn't mention the increase area for single interlock systems, 
it specifically mentions double interlock.  Don't confuse this with 12.5.1 as 
the 30% increase IS required for preaction systems in storage applications 
using density/area control mode sprinklers.

NFPA 13 2007, 
11.2.3.2.5* Dry Pipe and Double Interlock Preaction Systems.
For dry pipe systems and double interlock preaction systems,
the area of sprinkler operation shall be increased by 30 percent
without revising the density.




>From the NFPA 13 Handbook
11.2.3.2.5 The 30 percent area increase rule does not apply to preaction 
systems other than double interlock preaction
systems. Even though the pipe has no water in it, the delay in operation of 
non-interlock and single interlock systems 
is minimal, because the detection device typically responds to the fire sooner 
than the sprinkler. 
See the commentary following 7.3.2.1.


>From the NFPA 13 Handbook 
7.3.2.1 Preaction systems are addressed in 7.3.2.1. Both the single interlock 
and non-interlock systems
require only one event to occur before water is admitted to the system. The 
single interlock
system is activated by the release of the detection system. Sprinkler 
activation does not affect
this function. The non-interlock system is activated if either the detection 
system or a sprinkler
operates.
The double interlock preaction system requires two events to occur before water 
is
admitted to the system. One event consists of the activation of a device 
installed on the
supplemental detection system. The other event includes the operation of a 
sprinkler that
causes the maintained air pressure in the system to fall to a predetermined 
level, which is
similar to that of a dry pipe system. When one of these events occurs, the 
system activation
valve goes into a preset position. When the second event occurs, the valve 
opens, and water
enters the system. Water does not enter the system until both events occur. 
These two events
can occur in any order and result in the same outcome.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of sam b
Sent: Monday, June 29, 2009 7:49 AM
To: [email protected]
Subject: Preaction system : need help

Hiii friends

got a doubt regarding Preaction systems (specifically single interlocked 
system).

I am designing  a sprinkler system for a cultural /exhibition hall where the 
client needs preaction system for the entire area, The area is around 
14,100m2(1,52,000 ft2).
There are 4 no. risrers and I have considered 4 alarmcheckvalves for the total 
area and total sprinklers in the area is about 1650.

from NFPA 13 7.3.2.2 , I found" not more than 1000 sprinklers shall be 
controlled by one preaction valve."

does that mean u can have multiple zones controlled by single preaction valve?

In my case how many preaction valves should i consider, Is it 2 nos considering 
maxm 1000 per preaction valve.?

or 4 nos considering one along with each alarm check valve.?

Do I need to consider extra 30% that is to be considered for dry systems in my 
calculation??


Hope someone will clarify this for me..


Thanx in advance

Sam
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to