Where does it say I have to use an escutcheon on a pendant head?  If
recessed yes, a listed escutcheon for that head.  As long as I don't recess
the head seems like I wouldn't.  As long as the clg is above or right even
with the top of the arms the head wouldn't be recessed. Even if there is a
nominal gap around the threads, RC or pipe depending on elevation I don't
see where even filling/covering this gap is a requirement.  This isn't a
rated membrane penetration covered in IBC 712.3.2.  Even then it's a metal
escutcheon which might be a pipe ring not a sprinkler head escutcheon.     

 

Chris Cahill, P.E.