Greg,
I would consider them to be more like the obstruction you are talking about
and not included them in the calc. 

Bob Knight

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, August 04, 2009 2:27 PM
To: [email protected]
Subject: quick calc question

School gym with a stage at one end (with curtains, less than 50 feet tall).
At the very back of the stage there is a cut out on the back wall for
folding metal bleachers to fold into approximately 6' deep and 12' tall, the
remainder of the system is approximately 27' tall. There are 4 uprights in
the cut out (alcove) - 

Question - do they need to be included in the calcs, or would they be more
like the heads under an obstruction?

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
No virus found in this outgoing message.
Checked by AVG - www.avg.com
Version: 8.5.392 / Virus Database: 270.13.43/2281 - Release Date: 08/04/09 
05:57:00
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to