Greg:
 
I looked up a couple more things.  Can't find anything on vortex plates, but a 
Borda entrance (where the open end of the pipe is above the bottom of the tank, 
rather than flush) adds about 20 feet to your pipe length.  The open discharge, 
if you really had one, would add another 3 feet.  To be cautious, I would add 
50 feet for the entrance, discharge and vortex plate.  This knocks down your 
flow to 6950 gpm with zero residual, or about 4300 gpm at 35 psi residual.  
Still comfortably above your demand.

Contact me off-Forum if you need any of the reference material.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Thu, 8/6/09, David de Vries <[email protected]> wrote:


From: David de Vries <[email protected]>
Subject: RE: water storage tank
To: [email protected]
Date: Thursday, August 6, 2009, 11:08 AM



Greg:
 
You can make some assumptions about your situation to get into the ballpark.  
This is basically a civil engineering water supply problem -- an infinitely 
large reservoir discharging through an open pipe with a certain static head.
 
Use Hazen Williams and solve for Q.
 
Assume the 8" is Sch 30 steel, C=120, diameter 8.071, length the water is 
traveling is 140 feet. If it is an open pipe, the side-on pressure at discharge 
is zero (its all velocity pressure at that point).  Plug those numbers into HW 
and you get something like 8000 gpm at zero residual pressure.  So at 35 psi 
you've got a flow of about 4800 gpm.
 
Fine tune that using the actual pipe configuration as Craig pointed out, then 
Bernoulli and adjust for total energy (velocity pressure, static pressure and 
elevation pressure) and you can get a more precise answer.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Thu, 8/6/09, Greg McGahan <[email protected]> wrote:


From: Greg McGahan <[email protected]>
Subject: RE: water storage tank
To: [email protected]
Date: Thursday, August 6, 2009, 10:18 AM


I am getting info piecemeal from the engineering firm that is in charge of the 
tower. They say they don't 
Know what the residual pressure and flow will be when the tower is completed. 
We have a sprinkler system going in "next door" to the tower using the existing 
water from the old system. However, they have installed a 4" pipe with a 
hydrant instead of 6" (many years ago)and nobody knew until we dug it up.

Now we are flowing 600 gpm through a 4" pipe to our source and the calcs are 
too close for comfort. We are looking for a "guesstimate" of the available 
water at the base of the tower without any fittings or valves. I can add them 
in the 8" line from the base to the new tie in point where the systems tie 
together. We are talking about needing to pick up 5 to 10 psi  not 20 or 30, so 
as long as we are close we should be good. 

This really should fall on the EOR, but as is often the case in this region, if 
we want to finish the job on time, we have to get an answer immediately.

So I can say that I should reasonably be able to expect .156 x 140' = 22 lbs of 
loss from the tank to the bottom w/o fittings....therefore if we say we should 
reasonably expect 1,500 gpm at 35 psi?


Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, August 06, 2009 9:28 AM
To: [email protected]
Subject: RE: water storage tank

You're asking an open ended question.  Sorry for running you around in circles.

There are too many unknown variables here that are needed to make any kind of 
determination.

Like has been said, how much pipe, fittings, valves, elevations, what kind of 
discharge gpm, etc. etc, etc.

Plus the value at what tank level, since the tank head will affect the residual 
pressure.  

If you go by the flow required to produce a 10 fps velocity out of NFPA 24 for 
instance, that flow rate for an 8" would be 1560 gpm.

If you use cement lined DI pipe at 1560 gpm the pressure drop is .156 psi/10ft.

Ina real simplistic format, if you had 20 ft of pipe, static of 70 psi, flowing 
1560 gpm, the line loss equals .313 psi.  Use 1560 gpm and 69.6 psi for the 
K-factor which comes out to K=197.8.   Naturally the gpm will be slightly less 
than at the discharge but that difference would be negligible at these 
variables. 

This is all nominal since like I said the value will vary depending on tank 
level and other unknowns.  



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 06, 2009 9:37 AM
To: [email protected]
Subject: RE: water storage tank

Guys, I know all of the basic hydraulic stuff....I do NOT know the K factor of 
an 8" open pipe and don't feel comfortable guessing at formulas. I went to 
college and I know there is a formula that will easily tell you a reasonable 
expected flow and pressure. Bu that was a long time ago.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, August 06, 2009 8:29 AM
To: AFSA
Subject: Re: water storage tank

That depends on flow rate Greg. Higher flow = higher loss per ft.  Longer run = 
higher loss at specified flow rate.  




Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Greg McGahan" <[email protected]>

Date: Thu, 6 Aug 2009 08:06:45
To: <[email protected]>
Subject: RE: water storage tank


I know the static pressure. I need the RESIDUAL pressure and flow through an 
open 8" pipe at ground level.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, August 06, 2009 7:28 AM
To: [email protected]
Subject: RE: water storage tank

The formula is: ft of water x .433 = psi

So for 140 ft of head the approximate psi would be around 60 psi, at 70 ft it 
would be approximately 30, etc.

Note that this does not account for the loss through the tank outlet, vortex 
plate valves or piping loss.   

Find out what that 8" is.  Especially if it's a plastic.  Beware of HDPE.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Thursday, August 06, 2009 8:18 AM
To: [email protected]
Subject: water storage tank

We have a situation where a new water storage tank is being installed on a 
public utility system and I need some help if anyone can tell me the following:

New Tank - 140' high

8" pipe (unknown type) going straight to ground level

What is a reasonable expected flow and residual pressure?

Any help would be appreciated.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231 [email protected]


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)