Hello Mark,

This is existing we discovered during a walk through of a new location. Yes
it is in a stairwell, Been there for years they say.

Thursday, August 6, 2009, 1:35:53 PM, you wrote:

> If your express drain is in a stair shaft you may not be allowed to use PVC. 
> Something to check on.
> Mark at Aero 

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]on Behalf Of Charles
> Thurston
> Sent: Thursday, August 06, 2009 10:03 AM
> To: Autry, David
> Subject: Re[2]: Express Drain


> Hello David,

> DUHHHHH   Thanks I never thought to look there.

> Thursday, August 6, 2009, 12:34:17 PM, you wrote:

>> NFPA 13 (2002, Edition) 6.1.1.5
>> Components that do not affect system performance such as drain piping,
>> drain valves and signs shall not be required to be listed. 

>> David Autry
>> Plans Examiner
>> Nebraska State Fire Marshal's Office
>> 246 S. 14th Street
>> Lincoln, NE 68508
>> 402-471-9659
>> 402-471-3118 fax
>> www.sfm.ne.gov
>>  
>> ** Note new email address: [email protected]
>>  
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Charles 
>> Thurston
>> Sent: Thursday, August 06, 2009 11:30 AM
>> To: [email protected]
>> Subject: Express Drain

>> Hello sprinklerforum,

>>   I searched NFPA 13 and can not find anywhere it list the type of pipe
>>   required for an express drain. All I found is 1 size larger than the
>>   largest pipe tied into it. Does anybody know the section or if PVC
>>   "plumbing" pipe is allowed?







-- 
Best regards,
 Charles Thurston                            mailto:[email protected]
  Coastal Fire Protection