I was told years ago by a member on the NFPA #13 committee that if the entire 
remote area encompassed the entire sloped area the intent of the code was met. 
I have personally lived by that and never had any issues with engineers or 
AHJ's. I will say that I am referring to smaller sloped areas, not areas that 
are 1,499 sq ft....most of the ones I have seen in this case are 1,000 or less.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Thursday, August 06, 2009 6:16 PM
To: [email protected]
Subject: 30% increas in R.A. into non-sloped areas?

Just a quick question:I have an area with a 3:12 pitch so I must increase 
design area 30%.Since this area is only 1,000 sq. ft. would it be necessary to 
have the revised area size spill over into non-sloped areas? Or technically, 
could it just apply to the sloped area only?I usually do it the former 
mentioned way but I have a job that is right on the edge with the calcs and I'm 
looking to see if this is an option.ThanksRalphy


      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to