We are beginning to see more and more authorities require the class 1
outlets to supply 125 at 500 at roof and in the city of LA 125 psi at
300 gpm at all class 1 outlets. I seem to be finding that once you reach
a building height sufficient to require sprk/hose regulating valves then
they need to be installed all the way thru the roof. This because the
adjustment of the valves for the 125 psi setting does not allow you to
switch back to standard non regulating valves once you get to needed
elevation as you could in the past. Since the settings for the
adjustable valves require approx 230 psi/residual in to get 125psi
residual out, we are seeing what seems to me a pump sized much larger
than should be required. I have thought of installing pressure
regulating valves on the main vertical standpipes at a certain height,
but not sure this is good practice. Any thoughts? Are mfg companies
addressing this issue on a possible redesign?

Thanks for your time

 