Assuming that your system configuration would conform to trip times...

The talk is about 'floor area", correct?  So my assumption of your situation is 
that these dormers and eves extend the footprint of the area from 50K to 53K.  
If that's the case and it's not "overlapping" floor area (like a mezzanine type 
of thing), I'd see it as 2 systems required.  Given the consideration its 
borderline, with likely trip time issues, I'd be in line to provide what's best 
for the owner as opposed to split hairs on semantics.

On the concept that the areas have been sprayed and possibly don't require 
sprinkler protection, that doesn't omit the square footage from existing.  To 
me it doesn't seem much different than deleting the square footage of bathrooms 
under 55 square feet on dwelling units.

Just my $0.02

MPG




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Geoff Dyce
Sent: Wednesday, August 12, 2009 10:20 AM
To: [email protected]
Subject: attic

We have an attic that is 53,000 sq ft.  3000 sq ft has been sprayed with
fire retardant. (dormers and eves)  Can we say we have 50,000 sq ft or is
the area still considered 53,000 sq ft??  2 dry systems vs 1 dry system??



Geoffrey H. Dyce

Operations Manager/NICET IV

DELTA Fire Sprinklers, Inc.

A Veteran Owned Small Business

Ph:  407-328-3000 ext 143

Fx:  407-575-9991

E-Mail:  [email protected]





_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to