And in the end 13R is a life safety system. Commercial spaces are
public whether mercantile (M), business (B), assembly (A), education
(private K-12) (E), or mini-storage (not exclusive to tenant use) (S).
These spaces (and I think we can ignore E (public), F, H, I & U as
unlikely here) all require a13 system whether isolated from the
residential (R) portion or not. In some jurisdictions (not in mine if
I was king of one) 13R and 13 are allowed side by side or even with
the former on top of the latter but that is a local issue to discuss
with your building and fire officials. Then there are some
jurisdictions that allow V over I construction (again not allowed in
my perfect kingdom). That is Type V residential construction up to
four stories (with 13R sprinklers) on top of one or more stories
(story=building level above grade) of Type I construction (with 13
sprinklers). Crazy idea, which,  in my opinion, that takes a lot of
brain twisting vis-a-vis the IBC,  although most architects disagree
(which I think proves my point about it being a crazy idea).

On Wed, Aug 12, 2009 at 8:34 AM, Todd Williams<[email protected]> wrote:
> What that reference implies that the BFP will act as the check valve,
> which would normally be located between the connection to the FDC and
> the water supply (separate from the check valve on the FDC piping.)
>
>
> At 11:16 AM 8/12/2009, you wrote:
>>You are right about the double check I have up to now always put one on a 13
>>or 13R system but while looking for something else I came across the 6.7.1.6
>>reference and it made it sound like for a 13R system you did not need it.
>>
>>Karen Purvis
>>Senior Designer
>>Facility Systems Consultants
>>713 South Central Street,
>>Suite 101
>>Knoxville, TN 37902
>>ph.865-246-0164
>>fax 865-246-1084
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of George Church
>>Sent: Wednesday, August 12, 2009 11:24 AM
>>To: [email protected]
>>Subject: RE: Mixed occupancy
>>
>>First, I would not design a building with commercial space to 13R because
>>IMHO the building no longer is strictly residential in nature, the
>>commercial spaces don't sound like they will be restricted to
>>non-residential use incidental to the residential nature of the building. So
>>if this was my job, it'd be 13.
>>
>>The backflow requirements would be the same, a double check detector
>>assembly around here 99% of the time- whether 13 or 13R.
>>
>>Are you saying you don't install a backflow preventor on your 13R systems?
>>And the water purveyor turns it on and furnishes service to these buildings?
>>
>>glc
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of Karen Purvis
>>Sent: Wednesday, August 12, 2009 10:29 AM
>>To: [email protected]
>>Subject: RE: Mixed occupancy
>>
>>As for the building it is an apartment building with three floors of
>>apartments. The ground level has apartments and the front of the building
>>has space for 6 commercial locations. I don't know what will go in those
>>spaces. Since the majority of the building is apartments I designed as a
>>13R.
>>
>>The second question is in reference to 13R 6.7.1.6 "A listed backflow
>>prevention assembly shall be considered a check valve, and an additional
>>check valve shall not be required". In all my commercial builds I use a
>>double check backflow. So I guess my confusion is because there is mixed
>>occupancy would I use the double check because there IS commercial or just
>>use a single check BECAUSE its 13R.
>>
>>Karen Purvis
>>Senior Designer
>>Facility Systems Consultants
>>713 South Central Street,
>>Suite 101
>>Knoxville, TN 37902
>>ph.865-246-0164
>>fax 865-246-1084
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of George Church
>>Sent: Wednesday, August 12, 2009 10:23 AM
>>To: [email protected]
>>Subject: RE: Mixed occupancy
>>
>>Hmm. If the business portion of the occupancy is incidental to the
>>residential use of the building, as in a cafeteria serving a dorm, then you
>>drag over the couple items of #13 that 13R references for areas outside the
>>dwelling units. If it's a restaurant serving the general public but located
>>in a hotel, then the design is to #13 for the entire building- unless its
>>two buildings within the definitions of building separation in your
>>applicable building code. In either case, the riser is sized by the
>>hydraulic demand.
>>
>>I cannot imagine where you'd have a situation where the backflow preventor
>>is dependent upon 13 or 13R. In 13D you could omit the BFP in certain
>>instances, but that doesn't seem to be in your question. Why would the
>>occupancy change the need for backflow prevention in your mind? Water still
>>sitting there stagnant.
>>
>>glc
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of Karen Purvis
>>Sent: Wednesday, August 12, 2009 10:06 AM
>>To: [email protected]
>>Subject: Mixed occupancy
>>
>>These probably are questions everyone knows the answers to but I can't find
>>the answers:
>>
>>
>>
>>1.      If you have a mixed occupancy (residential & Business) and your
>>design is a 13R does your riser need to be at least a certain size or just
>>large enough to serve the hydraulic area?
>>2.      Because there is something other than residential in the building
>>would I not need a backflow on the riser?
>>
>>
>>
>>Karen Purvis
>>
>>Senior Designer
>>
>>Facility Systems Consultants
>>
>>713 South Central Street,
>>
>>Suite 101
>>
>>Knoxville, TN 37902
>>
>>ph.865-246-0164
>>
>>fax 865-246-1084
>>
>>
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to