I have a Viking dry pipe system, with a Viking D2 air maintenance device.  The 
air compressor is an EmGlow with a  Furnas 69HAU3 pressure switch.   I am 
unable to get the air past 26 PSI, which means the monitoring company reports a 
dry system trouble. 

My first step was to adjust the pressure switch, no difference.  The Furnas 
69HAU3 switch has a differential max of 6 - 16 PSI. The cut-in is 30 PSI and 
the cut-out is 40 PSI, which should work with a water pressure of 120 to 130 
PSI.   

I get my DeWalt air compressor out of the van and plumb it in.  I set the cut 
out to 40 PSI.  No change in the air pressure.  I set the cut-out to 50 PSI, no 
change in air pressure.  

 I  adjusted the D2 regulator.    I get the air pressure to 30 PSI by opening 
the by-pass valve.    I have no trouble on the Silent Knight panel.  

We tested the valve last month, every thing was OK
There is no accelerator.
The sprinkler valves are in the pool room, and they use liquid chlorine for the 
pool.  That means there is chlorine gas and the resultant corrosion.  

Now, do I replace the pressure switch &/or the pressure regulator? 

Douglas Hicks