>Today's Topics:
>
>   1. Main Drain (Jay Jay Blocker)
>   2. RE: Main Drain (Cliff Whitfield)
>   3. RE: Main Drain (Todd Williams)
>   4. Horizontal Sidewall Sprinklers (Jay White)
>   5. Re: Horizontal Sidewall Sprinklers (Sal Izzo (TECH- 103))
>   6. RE: Horizontal Sidewall Sprinklers (Steve Leyton)
>   7. Re: Horizontal Sidewall Sprinklers (Sal Izzo (TECH- 103))
>   8. Re: Main Drain (John Denhardt)
>
>
>----------------------------------------------------------------------
>
>Message: 1
>Date: Sun, 16 Aug 2009 17:46:12 -0700 (PDT)
>From: Jay Jay Blocker <[email protected]>
>Subject: Main Drain
>To: [email protected]
>Message-ID: <[email protected]>
>Content-Type: text/plain; charset=iso-8859-1
>
>I found where parts that dont affect the operation of a system dont have to be 
>listed.? Is there anywhere that says main drain piping has to be metal?
>
>J
>
>
>      
>
>------------------------------
>
>Message: 2
>Date: Sun, 16 Aug 2009 19:50:27 -0500
>From: "Cliff Whitfield" <[email protected]>
>Subject: RE: Main Drain
>To: <[email protected]>
>Message-ID: <[email protected]>
>Content-Type: text/plain;      charset="iso-8859-1"
>
>J,
>
>I think the big issue with non-metallic piping would be if it will meet code
>from a building code standpoint.  There are some cases where plastic is not
>acceptable in an exposed condition.  Check with your local plumbing and/or
>building inspector.
>
>Cliff Whitfield, SET
>Fire Design, Inc.
> 
>[email protected]
>www.fire-design.com
> 
> 
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jay Jay
>Blocker
>Sent: Sunday, August 16, 2009 7:46 PM
>To: [email protected]
>Subject: Main Drain
>
>I found where parts that dont affect the operation of a system dont have to
>be listed.? Is there anywhere that says main drain piping has to be metal?
>
>J
>
>
>      
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>
>------------------------------
>
>Message: 3
>Date: Sun, 16 Aug 2009 23:29:00 -0400
>From: Todd Williams <[email protected]>
>Subject: RE: Main Drain
>To: [email protected]
>Message-ID: <[email protected]>
>Content-Type: text/plain; charset="us-ascii"; format=flowed
>
>I've seen it used a few times (CPVC), but follow Cliff's advice and 
>check with the local authority
>
>
>
>At 08:50 PM 8/16/2009, you wrote:
>>J,
>>
>>I think the big issue with non-metallic piping would be if it will meet code
>>from a building code standpoint.  There are some cases where plastic is not
>>acceptable in an exposed condition.  Check with your local plumbing and/or
>>building inspector.
>>
>>Cliff Whitfield, SET
>>Fire Design, Inc.
>>
>>[email protected]
>>www.fire-design.com
>>
>>
>>-----Original Message-----
>>From: [email protected]
>>[mailto:[email protected]] On Behalf Of Jay Jay
>>Blocker
>>Sent: Sunday, August 16, 2009 7:46 PM
>>To: [email protected]
>>Subject: Main Drain
>>
>>I found where parts that dont affect the operation of a system dont have to
>>be listed.  Is there anywhere that says main drain piping has to be metal?
>>
>>J
>>
>>
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080  
>
>------------------------------
>
>Message: 4
>Date: Mon, 17 Aug 2009 08:16:07 -0500
>From: "Jay White" <[email protected]>
>Subject: Horizontal Sidewall Sprinklers
>To: <[email protected]>
>Message-ID:
>       <[email protected]>
>Content-Type: text/plain;      charset="us-ascii"
>
>I know there is a horizontal sidewall that covers extra hazard grp II, but
>is their a horizontal sidewall that covers group "A" plastics?
>
>Jay White
>Estimator/Design Manager
>Dynamic Fire Protection
>1807 Hwy. 25 South
>Starkville, MS 39759
>Phone: 662-324-1550
>Fax:       662-324-1545
>Cell:      662-312-2426
>
>
>
>
>------------------------------
>
>Message: 5
>Date: Mon, 17 Aug 2009 10:02:56 -0400
>From: "Sal Izzo (TECH- 103)" <[email protected]>
>Subject: Re: Horizontal Sidewall Sprinklers
>To: "[email protected]"
>       <[email protected]>
>Message-ID:
>       
> <961829597.260711.1250517798355.javamail....@bda053.bisx.prod.on.blackberry>
>       
>Content-Type: text/plain; charset="iso-8859-1"
>
>There is not.
>
>Regards,
>
>Salvatore Izzo PE
>Mgr-Tech Services
>Sent from my Verizon Wireless BlackBerry
>
>-----Original Message-----
>From: Jay White <[email protected]>
>
>Date: Mon, 17 Aug 2009 09:16:07 
>To: [email protected]<[email protected]>
>Subject: Horizontal Sidewall Sprinklers
>
>
>I know there is a horizontal sidewall that covers extra hazard grp II, but
>is their a horizontal sidewall that covers group "A" plastics?
>
>Jay White
>Estimator/Design Manager
>Dynamic Fire Protection
>1807 Hwy. 25 South
>Starkville, MS 39759
>Phone: 662-324-1550
>Fax:       662-324-1545
>Cell:      662-312-2426
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>------------------------------
>
>Message: 6
>Date: Mon, 17 Aug 2009 08:26:48 -0700
>From: "Steve Leyton" <[email protected]>
>Subject: RE: Horizontal Sidewall Sprinklers
>To: <[email protected]>
>Message-ID:
>       <6d5a59f81dd82b448ceddaf9db6cfeb99f4...@server.protectiondesign.local>
>Content-Type: text/plain;      charset="us-ascii"
>
>I think so.   Reliable makes a sidewall storage sprinkler, but you'll
>have to check the TDS or contact RASCO to confirm specific applications
>if any.
>
>Steve Leyton
>Protection Design & Consulting
>San Diego, CA
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jay White
>Sent: Monday, August 17, 2009 6:16 AM
>To: [email protected]
>Subject: Horizontal Sidewall Sprinklers
>
>I know there is a horizontal sidewall that covers extra hazard grp II,
>but
>is their a horizontal sidewall that covers group "A" plastics?
>
>Jay White
>Estimator/Design Manager
>Dynamic Fire Protection
>1807 Hwy. 25 South
>Starkville, MS 39759
>Phone: 662-324-1550
>Fax:       662-324-1545
>Cell:      662-312-2426
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
> 
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 4341 (20090817) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
> 
> 
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 4342 (20090817) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
> 
>
>
>------------------------------
>
>Message: 7
>Date: Mon, 17 Aug 2009 11:49:17 -0400
>From: "Sal Izzo (TECH- 103)" <[email protected]>
>Subject: Re: Horizontal Sidewall Sprinklers
>To: "[email protected]"
>       <[email protected]>
>Message-ID:
>       
> <516375353.265123.1250524159041.javamail....@bda053.bisx.prod.on.blackberry>
>       
>Content-Type: text/plain; charset="iso-8859-1"
>
>The MBEC-14 can be used as an extra hazard hsw spinkler for occupancies having 
>misc. storage only; it is not a storage sprinkler, nor can it be used for Grp 
>A Plastics.  
>
>Regards,
>
>Salvatore Izzo PE
>Mgr-Tech. Services
>Sent from my Verizon Wireless BlackBerry
>
>-----Original Message-----
>From: Steve Leyton <[email protected]>
>
>Date: Mon, 17 Aug 2009 11:26:48 
>To: [email protected]<[email protected]>
>Subject: RE: Horizontal Sidewall Sprinklers
>
>
>I think so.   Reliable makes a sidewall storage sprinkler, but you'll
>have to check the TDS or contact RASCO to confirm specific applications
>if any.
>
>Steve Leyton
>Protection Design & Consulting
>San Diego, CA
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Jay White
>Sent: Monday, August 17, 2009 6:16 AM
>To: [email protected]
>Subject: Horizontal Sidewall Sprinklers
>
>I know there is a horizontal sidewall that covers extra hazard grp II,
>but
>is their a horizontal sidewall that covers group "A" plastics?
>
>Jay White
>Estimator/Design Manager
>Dynamic Fire Protection
>1807 Hwy. 25 South
>Starkville, MS 39759
>Phone: 662-324-1550
>Fax:       662-324-1545
>Cell:      662-312-2426
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
> 
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 4341 (20090817)__________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
> 
> 
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 4342 (20090817)__________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
> 
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>------------------------------
>
>Message: 8
>Date: Sun, 16 Aug 2009 21:11:56 -0400
>From: "John Denhardt" <[email protected]>
>Subject: Re: Main Drain
>To: <[email protected]>
>Message-ID:
>       
> <287576106-1250472413-cardhu_decombobulator_blackberry.rim.net-6470558...@bxe1225.bisx.prod.on.blackberry>
>       
>Content-Type: text/plain;      charset="Windows-1252"
>
>No, not in NFPA 13.
>
>John
>Sent from my BlackBerry? smartphone with Nextel Direct Connect
>
>-----Original Message-----
>From: Jay Jay Blocker <[email protected]>
>
>Date: Sun, 16 Aug 2009 17:46:12 
>To: <[email protected]>
>Subject: Main Drain
>
>
>I found where parts that dont affect the operation of a system dont have to be 
>listed.? Is there anywhere that says main drain piping has to be metal?
>
>J
>
>
>      
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>------------------------------
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>End of Sprinklerforum Digest, Vol 46, Issue 16
>**********************************************