Thanks 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
McCullough
Sent: Tuesday, September 29, 2009 8:48 PM
To: [email protected]
Subject: RE: Pressure reducing hose valves - NFPA 25

I believe a bucket will do.
 
13.5 Pressure Reducing Valves and Relief Valves
13.5.1.3 A partial flow test adequate to move the valve from its seat
shall be conducted annually.
Handbook Commentary: The test required in 13.5.1.3 is intended to
exercise the valve and ensure that it is not obstructed and will
re-seat.
 
Similar text is in 13.5.2 Hose Connection Pressure Reducing Valves and
13.5.3 Hose Rack Assembly Pressure Reducing Valves.
and 13.5.4 Master Pressure Reducing Valves.
 
Bobby
 

________________________________

From: [email protected] on behalf of Ron Greenman
Sent: Tue 9/29/2009 4:39 PM
To: [email protected]
Subject: Re: Pressure reducing hose valves - NFPA 25



Reference Dewayne. What section and edition says that? And are you
actually talking pressure reducing or pressure regulating valve? I'd
love to help but when we get potentially partial quotations from
undefined sources it's just too much work to have to search all the 25s
and guess we're talking about something in the standpipe section and
then find exactly what sentence is quoted. I like to see where the
sentence is in the hierarchy as well as the information surrounding it
and possibly if there's commentary. The questions I can typically answer
off the top of my head without equivocation are typically not the type
asked by this learned assemblage.

On Tue, Sep 29, 2009 at 10:44 AM, Dewayne Martinez <[email protected]>
wrote:
> NFPA 25 says that "A partial flow test adequate to move the valve from

> it's seat shall be conducted annually".
> Is this simply opening the pressure reducing hose valve and flowing 
> some water into a bucket or should it be hooked up to the 3" drain
riser?
> Thanks,
> Dewayne
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to