Thanks -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby McCullough Sent: Tuesday, September 29, 2009 8:48 PM To: [email protected] Subject: RE: Pressure reducing hose valves - NFPA 25
I believe a bucket will do. 13.5 Pressure Reducing Valves and Relief Valves 13.5.1.3 A partial flow test adequate to move the valve from its seat shall be conducted annually. Handbook Commentary: The test required in 13.5.1.3 is intended to exercise the valve and ensure that it is not obstructed and will re-seat. Similar text is in 13.5.2 Hose Connection Pressure Reducing Valves and 13.5.3 Hose Rack Assembly Pressure Reducing Valves. and 13.5.4 Master Pressure Reducing Valves. Bobby ________________________________ From: [email protected] on behalf of Ron Greenman Sent: Tue 9/29/2009 4:39 PM To: [email protected] Subject: Re: Pressure reducing hose valves - NFPA 25 Reference Dewayne. What section and edition says that? And are you actually talking pressure reducing or pressure regulating valve? I'd love to help but when we get potentially partial quotations from undefined sources it's just too much work to have to search all the 25s and guess we're talking about something in the standpipe section and then find exactly what sentence is quoted. I like to see where the sentence is in the hierarchy as well as the information surrounding it and possibly if there's commentary. The questions I can typically answer off the top of my head without equivocation are typically not the type asked by this learned assemblage. On Tue, Sep 29, 2009 at 10:44 AM, Dewayne Martinez <[email protected]> wrote: > NFPA 25 says that "A partial flow test adequate to move the valve from > it's seat shall be conducted annually". > Is this simply opening the pressure reducing hose valve and flowing > some water into a bucket or should it be hooked up to the 3" drain riser? > Thanks, > Dewayne > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)