I'll defer to your more recent memory of data presented in a more formal
setting- and perhaps another will chime in. I trust I've thanked Marriott
for their diligence sufficiently that they won't sue for libel.

We installed sprinklers in the Stouffers-Valley Forge as a retrofit, maybe
1987, I don't know if the driving force was corporate focus on avoiding
future catastrophe or satisfying a determined fire official known to roam
those UMT streets. I'll see John next week and will ask. He'll likely
remember the details of the WP fire.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David de
Vries
Sent: Wednesday, September 30, 2009 8:35 PM
To: [email protected]
Subject: Re: fatal fire from Combustible concelaed space ?


George:
 
We case-studied that fire in engineering school -- a long time ago.  I do
not recall the fire developing in a ceiling space, but there was only one
means of egress from the conference room and there were multiple
fatalities.  I believe the fire was deliberately set and I thought it was a
Stouffer's Inn, not Marriott.
 
BTW, Marriott has not worked those older Residence Inns out of their
system.  When traveling with the family pooch I have stayed at one near my
parents' home several times over the last 10 years, including once last
month.  It remains unsprinklered and an RI.  I request a first floor room.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 


--- On Wed, 9/30/09, George Church <[email protected]> wrote:


From: George Church <[email protected]>
Subject: fatal fire from Combustible concelaed space ?
To: [email protected]
Date: Wednesday, September 30, 2009, 5:17 PM


I'd ask the AHJ for HIS interpretation before you go dancing off with the
creatures that jumped outa Pandora's box, lest they lead you astray. 

I'm not a PE, but if I was entitled to an opinion, I wouldn't think the fuel
loading of 2x4's @ 16" on center is going to be sufficient to feed an
inferno.

And as for history of fires above ceilings killing people, does anyone have
a better recollection of what led to Marriott's premier position WRT concern
for fire sprinklers back in White Plains, NY? 

My memory is that a fire broke out from above a ceiling in an unsprinklered
meeting room area, killing the entire management team of a firm in the
meeting room and Marriott brass said "Never again" and they invested
millions into developing the residential sprinkler concept- AND APPLYING IT
WORLD-WIDE CONSISTENTLY - so that the traveling public that "gets it" and
wants to stay in sprinklered hotels can simply chose a Marriott brand
anywhere* and they'll be safe from fire. 

So if someone can validate what I recall happened in White Plains
(1981+/-?), that could be a large disaster that shouldn't be repeated. 

I don't know that I'd lose sleep over unsprinklered TJI's above drywall and
no 3,000 SF MRA around me. Open wood joists without separation or
compartmentalization- yeah, that would bother me, whole different level of
fuel load and oxygen available- but I'm not an engineer, just a guy that
tries to stay in sprinklered hotels and avoid dying a really ironic death.

* one caveat is that a few years ago I learned about 10% of the older
Residence Inns were unsprinklered, and they were being worked out of the
system. One of them is in Valley Forge, PA which my wife noticed before I
did, surprisingly enough.

George Church
Rowe Sprinkler
Marriott Gold Level ;) - support those that support us!

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Wednesday, September 30, 2009 5:54 PM
To: [email protected]; [email protected]
Subject: Re: A.8.15.1.2.1

Travis,

Hopefully you defined the date of the plans and specs you were given
to bid from. If that set shows steel studding supporting the soffiting
and the GC used wood then you have a legitimate change order if this
change does turn what was an exempt concealed space into a non-exempt
concealed space. And the change to steel pipe would be included
because the 36" limitation of the heads you wouldn't have needed to
put in in the first place were never an issue at bid time.

On Wed, Sep 30, 2009 at 2:20 PM, Travis Mack <[email protected]> wrote:
> Yeah.  This is one of those that "I can't define it, but I know it when I
> see it" things.  My feeling is that it is going to need sprinklers.  I
> haven't seen the space yet, just what the fitter and project manager
> relayed today.
>
> Anyway, the rooms are like a typical Holiday Inn 1st floor: conference
> rooms, offices, etc.  The gyp goes to the deck in all of the rooms for the
> walls, so that is not an issue.  For example, a conference room is 20x40.
> It has a 3' soffit at the perimeter that is framed in wood (2x4 @ 16" on
> center) to create the soffit.  Does that qualify as minor combustibles?
> Not sure, but I don't want to make the judgment call.  That is above my
> pay grade.
>
> We just realized another issue.  The bottom of the concrete deck is
> 13'-8".  This ceiling is at 10'-0".  This exceeds the 36" max dimension
> allowed for the specially listed concealed space sprinklers.  So, all of
> the piping would have to go to steel and use standard spray sprinklers.
> The project is turning into Pandora's box.  I am not fully sure if the
> specially listed concealed space sprinklers could even be used in this
> application if it met the 36" requirement.  I have to research that a bit
> more.
>
>> I agree with Todd if it's the walls = sprinkler all.
>>
>> But I think the question is limited to gyp CIELINGS and SOFFITS.  In that
>> case I think '02-8.14.1.5 can help, Localized Protection of Exposed
>> Combustible Construction.
>>
>> I do think you have to deal with it either way.  Unless the area involved
>> is
>> really, really small like a few sq.ft. separated by 20's of feet to the
>> next
>> few sq.ft. IDK?  Without seeing it can't advise on the judgment call on
>> how
>> small is small.
>>
>>
>>
>> Chris Cahill, P.E.
>> Fire Protection Engineer
>> Sentry Fire Protection, Inc.
>>
>> 763-658-4483
>> 763-658-4921 fax
>>
>> Email: [email protected]
>>
>> Mail: P.O. Box 69
>>         Waverly, MN 55390
>>
>> Location: 4439 Hwy 12 SW
>>               Waverly, MN 55390
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd
>> Williams
>> Sent: Wednesday, September 30, 2009 3:03 PM
>> To: [email protected]
>> Subject: Re: A.8.15.1.2.1
>>
>> Travis,
>>
>> I've always looked at "limited combustible" as a subjective term. You
>> know what isn't, but not sure what is. If you have 2x's at 16" oc all
>> over the place, chances are it isn't "limited combustible". If they
>> used a few pieces of wood to support and ceiling fixture in an
>> otherwise N/C space, that would be limited. I usually work with the
>> AHJ to come up with a consensus. That also stops a lot of arguments.
>>
>> Todd
>>
>> At 03:10 PM 9/30/2009, you wrote:
>>>We have a hotel designed per NFPA 13.  The 2nd floor is concrete.  The
>>>building plans showed the gyp board ceilings to be framed with non
>>>combustible channel.  Therefore, the space above the 1st floor ceilings
>>>would be a non-combustible concealed space.  However, when the fitters
>>>arrived on site, it was found that the GC has taken it upon himself to
>> frame
>>>all of the gyp board ceilings / soffits on the first floor with wood.
>> Would
>>>this be considered minimal / minor quantities of non structural wood?
>>> What
>>>is a decent defining factor for minor quantities?  If sprinklers are
>>>required, the GC realized today that a change order is forth-coming.  It
>>> is
>>>just an issue of scheduling to go back and get the first floor redesigned
>> to
>>>accomodate the new construction.  This project was also done with CPVC
>>>piping, so we would have to go with the specially listed concealed space
>>>sprinklers to protect these areas.
>>>
>>>8.15.1.2.1*  Concealed spaces of noncombustible and limited-combustible
>>>construction with minimal combustible loading having no access shall not
>>>require sprinkler protection. The space shall be considered a concealed
>>>space even with small openings such as those used as return air for a
>>>plenum. (For additional information on combustible loading, see
>>>A.8.15.1.2.1.)
>>>
>>>A.8.15.1.2.1  Minor quantities of combustible materials such as but not
>>>limited to: cabling, nonmetallic plumbing piping, non-structural wood,
>>> etc.
>>>can be present in concealed spaces constructed of limited or
>>> noncombustible
>>>materials but should not typically be viewed as requiring sprinklers (see
>>>8.15.1.1). For example, it is not the intent of this section to require
>>>sprinklers, which would not otherwise be required, in the interstitial
>> space
>>>of a typical office building solely due to the presence of the usual
>>> amount
>>>of cabling within the space.  The threshold value at which sprinklers
>> become
>>>necessary in the concealed space is not defined.
>>>
>>>Thanks in advance for any help / opinions.
>>>
>>>Travis Mack
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>>For Technical Assistance, send an email to: [email protected]
>>>
>>>To Unsubscribe, send an email to:[email protected]
>>>(Put the word unsubscribe in the subject field)
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, Connecticut
>> www.fpdc.com
>> 860.535.2080
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
> --
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to