Charles,

Not sure about 13, but it's certainly in the '07 edition of 13R:

6.7.7.1.5.7 Small potentially blocked or shadowed floor areas shall be 
permitted on a horizontal plane in compartments of 800 ft2 (74.3 m2) or 
less as long as all of the following conditions are met. For purposes of 
simplified calculations, assume in this theoretical case that the water 
discharging from a sprinkler travels in a straight line only.

(1) The maximum area of any single individual contiguous shadowed floor 
area, regardless of geometric configuration, shall not exceed 3 ft2 
(0.28 m2).

(2) The maximum area summation of any number of individual shadowed 
floor areas shall not exceed 12 ft2 (1.11 m2) per compartment.

(3) The maximum total summation of shadowed floor areas and allowances 
made by 6.7.7.1.5.3 shall not exceed 30 ft2 (2.79 m2) per dwelling unit.

-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Charles Thurston wrote:
> Hello sprinklerforum,
>
>   Somewhere I have seen something in NFPA 13 2007 about small shadow areas 
> caused by a protruding wall. I have been searching but was unable to find the 
> section, Anybody know off hand where it is?
>
> Thanks
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
  • Shadow Areas Charles Thurston
    • Re: Shadow Areas ParsleyConsulting

Reply via email to