Sounds like the old Central bi-metallic disc on/off heads.  The ones that
had a habit of cold-soldering themselves.  I'm sitting here staring at one
on my bookshelf that I snagged from a dusty corner of our shop warehouse
three years ago.

On Thu, Oct 1, 2009 at 5:16 PM, Chris Gaut <[email protected]> wrote:

> Tired to send this early so it may come through again later......Just as an
> FYI....(and part of the "rest of the story"), I contact the Fire Marshal
> for
> his opinion and asked if there was a way to shed a different light on what
> happened and the negative press of the sprinkler system.  Here was the
> email
> reply I was sent. Hopefully he can turn the table a little.
>  -Chris
>
> ----------------------------------------------------------------------------
>
> Early report is a single head failure, 27 year old specialty head designed
> to actuate at 165 degree's then shut off when temp drops below 165.
> Designed
> for applications like the historical society.
>
> Appears to be an O-ring failure.
>
> More soon with an updated press release.
>
> Thanks.
> Battalion Chief Steven Sapp
> Fire Marshal
> Columbia Fire Department
> 201 Orr Street
> Columbia, Month 65201
> 573-874-7556
> [email protected]
> www.gocolumbiamo.com/Fire
> ---------------------------------------
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Thursday, October 01, 2009 4:13 PM
> To: [email protected]
> Subject: RE: Not again.... or AKA RE: Now we know...it was so old it
> disintegrated....
>
> This was the original link that had the extra comments.
>
> Obviously we're not privy to what's going on behind the scenes based on the
> first commentator's remarks.
>
>
>
>
> http://www.columbiamissourian.com/stories/2009/10/01/fire-sprinkler-soaks-mi
> ssouri-state-historical-society-documents/<http://www.columbiamissourian.com/stories/2009/10/01/fire-sprinkler-soaks-mi%0Assouri-state-historical-society-documents/>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to