Don't look now, but City of San Diego requires a certified RPZ assembly
on all new sprinklered domestic services.   We still end up with a check
at the riser because the BFP is at the property line ...

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Wednesday, October 21, 2009 5:06 AM
To: [email protected]
Subject: RE: 13D and backflow preventers

I can see where black steel pipe in the basement might be less than
desirable if connected to the rest of the plumbing, but a pair of
rubber-seated checks could address that at lower cost, and without the
friction loss of spring-loaded clappers inherent in a BFP.

As with so many of these requests, the knee-jerk reaction should be:
"Could you show me the regulation so we can be certain we are complying
with
it in its entirety?"

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Wednesday, October 21, 2009 6:24 AM
To: [email protected]
Subject: 13D and backflow preventers

I did a design a couple of years ago for a group home based on NFPA 
13D (2002). We have a single copper feed from the public supply for 
both domestic and fire. The basement has steel pipe and the upper 
floors have CPVC. Now, the water company is coming back and saying 
that a backflow preventer is required on the system because of the 
different materials used on the system. Supposedly the State of CT is 
requiring it, although I've never heard of it before. Anybody run 
into this in other jurisdictions?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4529 (20091021) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 4529 (20091021) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to