"This looks like antifreeze systems need to be investigated by NIST to
determine the dangers."
 
Rahe, was that said tongue in cheek?  Yes, ethylene glycol is a combustible 
liquid, but the important point of measure is the flashpoint of the mixture 
with water.  Off hand I do not know what that would be, but water mixed with 
isopropanol raises the flashpoint significantly.  Try lighting a glass of wine 
vs 151 proof rum.
 
A few years back there was a Swedish study of antifreeze in systems.  There was 
a measurable increase in burning rate briefly upon system discharge until the 
water behind the antifreeze got there.  My recollection is that it was deemed 
not significant compared to the delay of dry or pre-action systems.
 
Bottom line from reading that article is that they are looking at all 
possibilities, as is recommended by NFPA 921, and then ruling them out as they 
gather information.  Pouring water on burning grease that is well above the 
boiling point of water is likely to create quite a volume of burning grease 
when the water sinks to the bottom of the pan and then flashes to vapor.  That 
will probably end up being the focus of their investigation.


Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Thu, 10/22/09, [email protected] <[email protected]> wrote:


From: [email protected] <[email protected]>
Subject: Re: Report: Antifreeze sprinkler system may have contributed to fatal 
explosion
To: [email protected], "Richard Mote" <[email protected]>
Date: Thursday, October 22, 2009, 3:44 PM


Why is there an antifreeze system inside a building? Not knowing what was
used in the system, here is the info from the ethylene glycol MSDS:

Section 5: Fire and Explosion Data

Flammability of the Product: May be combustible at high temperature.

Auto-Ignition Temperature: 398°C (748.4°F)

Flash Points: CLOSED CUP: 111°C (231.8°F). (Tagliabue.)

Flammable Limits: LOWER: 3.2%

Products of Combustion: These products are carbon oxides (CO, CO2).

Fire Hazards in Presence of Various Substances:
Slightly flammable to flammable in presence of open flames and sparks, of
heat.
Non-flammable in presence of shocks.

This looks like antifreeze systems need to be investigated by NIST to
determine the dangers.

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102



                                                                           
                                                                           
             "Richard Mote"                                                
             <rich...@rowespri                                          To 
             nkler.com>                <[email protected]>  
             Sent by:                                                   cc 
             sprinklerforum-bo                                             
             un...@firesprinkl                                     Subject 
             er.org                    Report: Antifreeze sprinkler system 
                                       may have contributed to fatal       
                                       explosion                           
             10/22/2009 03:18                                              
             PM                                                            
                                                                           
                                                                           
             Please respond to                                             
             sprinklerfo...@fi                                             
             resprinkler.org;                                              
             Please respond to                                             
               Richard Mote                                                
             <rich...@rowespri                                             
                nkler.com>                                                 
                                                                           
                                                                           




Say What?

http://www.sierrasun.com/article/20091020/NEWS/910169995/1066&ParentProfile=1051


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to