Dwayne,
The other option you may be able to apply is the allowance 13 provides for
offsetting from center.  L = 4ab/a+b.  Depending if you are able to install
off center, and based on the pipe size hung you may be able to use a lower
modulus number.  This might help you size the trap member where you would
like it to be size wise.


Bob Knight

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Thursday, October 22, 2009 4:14 PM
To: [email protected]
Subject: RE: trapeze hanger

I wouldn't interpolate it, either jump up to the 6' span or you can calc it.
If you want I can fax you an example.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]] 
Sent: Thursday, October 22, 2009 2:52 PM
To: [email protected]
Subject: trapeze hanger

Can you interpolate the values for the section modulus for trapeze
hangers in table 9.1.1.6.1(b) for a span not shown?
IE: I have a 5'-6" span
I did not see a section allowing it.
Thanks,
Dewayne

-------------- next part --------------

No virus found in this outgoing message.
Checked by AVG - www.avg.com 
Version: 8.5.423 / Virus Database: 270.14.26/2451 - Release Date: 10/22/09 
08:51:00
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to