Dwayne, The other option you may be able to apply is the allowance 13 provides for offsetting from center. L = 4ab/a+b. Depending if you are able to install off center, and based on the pipe size hung you may be able to use a lower modulus number. This might help you size the trap member where you would like it to be size wise.
Bob Knight -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jim Johnston Sent: Thursday, October 22, 2009 4:14 PM To: [email protected] Subject: RE: trapeze hanger I wouldn't interpolate it, either jump up to the 6' span or you can calc it. If you want I can fax you an example. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180 [email protected] -----Original Message----- From: Dewayne Martinez [mailto:[email protected]] Sent: Thursday, October 22, 2009 2:52 PM To: [email protected] Subject: trapeze hanger Can you interpolate the values for the section modulus for trapeze hangers in table 9.1.1.6.1(b) for a span not shown? IE: I have a 5'-6" span I did not see a section allowing it. Thanks, Dewayne -------------- next part -------------- No virus found in this outgoing message. Checked by AVG - www.avg.com Version: 8.5.423 / Virus Database: 270.14.26/2451 - Release Date: 10/22/09 08:51:00 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)