I was at a location yesterday where they have had a problem of splits in CPVC pipe in a basement. The fire pump churn is roughly 175 psi but the jockey pump is set at 150 psi. Would repeated water hammer from weekly/quarterly/annual tests create enough fatigue to cause failure?
Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)