It's not so much about if secondary power is available as it is about whether 
secondary power is necessary.  

If the primary power source is considered unreliable or if there are issues 
with the capability of the local fire department (NFPA 20, 9.3) then secondary 
power is to be provided.  If you have a diesel pump this requirement does not 
apply.

Also refer to NFPA 20, 10.8 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jay White
Sent: Thursday, October 29, 2009 3:12 PM
To: [email protected]
Subject: Transfer switches?

Is their a simple explanation in NFPA about requirements? If secondary power 
available should they be installed?

Jay White
Dynamic Fire Protection
1807 Hwy. 25 South
Starkville, MS 39759

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to