Any possibility of lowering the system, or even just parts of it,  14-15". 
Just a thought.

Thomas

----- Original Message ----- 
From: "Forest Wilson" <[email protected]>
To: <[email protected]>
Sent: Friday, October 30, 2009 4:15 PM
Subject: Re: Does Anyone manufacture Dry Sprinklers longer than 60"?


>
> Thank you all for the response about Viking Dry heads.
> I spoke with the AHJ- State Fire Marshal office and they stated they will 
> not accept installation of any heads that are not UL listed.
> UL lists heads up to 48" in length, so we will have to re-pipe this dry 
> system and use shorter length dry heads.
>
>
> Forest Wilson
>
> Project Manager
> Cherokee Fire Protection Co.
> 3195 Dayton Xenia Rd Ste 900
> Dayton OH 45434
>
> ph: 937-376-2333
> fx: 614-455-4324
> cell: 937-307-5647
>
>
> .
>
>
>
> Visit our blog: www.cherokee-fire.blogspot.com
>
>
>
>
>
>
>
> NOTICE: The information contained in this email is intended to be solely 
> for the use of the named individual or entity to which it is directed and 
> may contain information that is privileged or otherwise confidential. It 
> is not intended for transmission to, or receipt by, anyone other than the 
> named addressee (or a person authorized to deliver it to the named 
> addressee). It should not be copied or forwarded to any unauthorized 
> persons. If you have received this electronic mail transmission in error, 
> please delete it from your system without copying or forwarding it, and 
> notify the sender of the error by reply email or by calling Cherokee Fire 
> Protection Co. at 888-347-3079 toll free.
>
>
> -----Original Message-----
> From: Lori Kitchen <[email protected]>
> To: [email protected]
> Sent: Fri, Oct 30, 2009 1:59 pm
> Subject: RE: Does Anyone manufacture Dry Sprinklers longer than 60"?
>
>
>
> Viking makes them up to 65"...but it does not have any listings.  The AHJ
> as to sign off on their use if we use them here as well.
>
> ori Kitchen
> P, Service & Maintenence Division
> hitewater Fire Sprinkler
> 316-295-4120 (office)
> 16-295-4162 (fax)
>
> -----Original Message-----
> rom: [email protected]
> mailto:[email protected]] On Behalf Of Forest 
> Wilson
> ent: Friday, October 30, 2009 11:17 AM
> o: [email protected]
> ubject: Does Anyone manufacture Dry Sprinklers longer than 60"?
>
> oes anyone know of a source for dry pendant sprinkler longer than 60"?
> pecifically 62, 62.5, and 63 inches long?
> property we work for has old Central dry heads, the Fire Marshal says to
> eplace them, and the city says to repipe we need a permit, engineered
> rawings, etc...I'm hoping we can just replace them to save the owner 
> money.
>
> orest Wilson
> Project Manager
> herokee Fire Protection Co.
> 195 Dayton Xenia Rd Ste 900
> ayton OH 45434
> ph: 937-376-2333
> x: 614-455-4324
> ell: 937-307-5647
>
>
>
> Visit our blog: www.cherokee-fire.blogspot.com
>
>
>
> NOTICE: The information contained in this email is intended to be solely 
> for
> he use of the named individual or entity to which it is directed and may
> ontain information that is privileged or otherwise confidential. It is not
> ntended for transmission to, or receipt by, anyone other than the named
> ddressee (or a person authorized to deliver it to the named addressee). It
> hould not be copied or forwarded to any unauthorized persons. If you have
> eceived this electronic mail transmission in error, please delete it from
> our system without copying or forwarding it, and notify the sender of the
> rror by reply email or by calling Cherokee Fire Protection Co. at
> 88-347-3079 toll free.
> ______________________________________________
> prinklerforum mailing list
> [email protected]
> ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email to:[email protected]
> Put the word unsubscribe in the subject field)
> _______________________________________________
> prinklerforum mailing list
> [email protected]
> ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
> To Unsubscribe, send an email to:[email protected]
> Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)


--------------------------------------------------------------------------------



Internal Virus Database is out of date.
Checked by AVG - www.avg.com
Version: 8.5.374 / Virus Database: 270.12.69/2176 - Release Date: 06/14/09 
17:54:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to