First of all thanks to everyone that helped clarify the density question earlier. Now this question: On the Tyco cut sheet for their ESFR-25 head there is a note that says "where the depths of solid members ...... exceed 12", ESFR heads shall be installed in each channel formed by the structural members." I understand this comes from NFPA-13 8.4.6.3 (07). Under section 8.12.4.1 "Distance Below Ceilings" for this particular head, K=25.2, it allows the deflector to be up to 18" down from the deck. Is this only applicable in unobstructed construction? If so I don't see where it says that. My problem is that on this particular job the ceiling is made out of concrete tee's that are 16" deep, ceiling is 41'. I was hoping to be able to run the branch lines up in the tee's using the pendent position and getting the deflector down at 18", spacing lines at 10' apart. Am I doomed?
Regards, _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)