First of all thanks to everyone that helped clarify the density question
earlier. Now this question: On the Tyco cut sheet for their ESFR-25 head
there is a note that says "where the depths of solid members ...... exceed
12", ESFR heads shall be installed in each channel formed by the structural
members." I understand this comes from NFPA-13 8.4.6.3 (07). Under section
8.12.4.1 "Distance Below Ceilings" for this particular head, K=25.2, it
allows the deflector to be up to 18" down from the deck. Is this only
applicable in unobstructed construction? If so I don't see where it says
that. My problem is that on this particular job the ceiling is made out of
concrete tee's that are 16" deep, ceiling is 41'. I was hoping to be able to
run the branch lines up in the tee's using the pendent position and getting
the deflector down at 18", spacing lines at 10' apart. Am I doomed?
 

Regards,

 
 