We were involved in one a few years back that was around 28,000 sq.ft. and was classified as an F-1 occupancy (2003 IBC). They dump municipal trash, which is pushed onto conveyors that ultimately bring it through a wall to be compacted into bales. (Improved efficiency in the loading of the landfill, reduces flying garbage, and sets them up for the day that the landfill is full and they need to haul to another site.
We required sprinkler protection within the return air ducts due to anticipated dust loading; protection throughout the tip floor and dump pit required some creativity, because there is no cut-n-dry answer just looking at NFPA 13. A large chunk of the garbage is paper and paper-related items such as box-board, etc. But there are some plastics inevitably mixed in. I looked at FM's guidelines for baled paper, as well as solid-piled plastics - since neither of these fit exactly, I deduced my own scheme. I believe we ended up with 0.3/3,000 using 11.2K sprinklers on 100 sq.ft. spacing. This should work well also for a fire involving one of the larger vehicles you'd see in the building (flat-bed tractor/trailer, garbage trucks, front-end loader-type equipment). This is one of those jobs where it was nice being on the engineering side of the fence, because I don't know how I would have bid it were I in contracting at the time. (let's just hope the design works if it's ever needed) Mark A. Sornsin, PE Fire Protection Engineer Ulteig Engineers, Inc. Fargo, ND [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ryan Peterson Sent: Friday, November 20, 2009 8:35 AM To: [email protected] Subject: Waste Transfer Stations Group We are currently looking at a waste transfer station. I cannot find any requirements for fire protection. Does anyone know if there are requirements out there? Thanks in advance Ryan Peterson Wayne Automatic Fire Sprinklers _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)