Greg,

How about north and west? Seismic zones and about 15F all week. Not
all winter weather but at least once a year. Eastern washington colder
yet and still seismic.

On Fri, Dec 11, 2009 at 12:24 PM, Greg McGahan <g...@livingwaterfp.com> wrote:
> My 2 cents worth is thus: We life in a climate where a real freeze only 
> occurs every 10 or so years, the last true hard freeze here in which there 
> was significant damage from the temps was around 96 or 97. Nearly all of the 
> corrosion that we see on wet and dry systems is from the outside in not from 
> the inside out. I have never seen a dry system that was seriously damaged 
> from roll grooved pipe, or MIC in this area. I would almost say that the 
> money spent on a large percentage of dry systems here is not well spent 
> barring the paranormal freeze.
>
> I think the issue is that as the use of the NFPA codes has expanded, and the 
> rules have been better defined and more issues have been addressed, that the 
> fact that there is HUGE diversity in the practical needs across the country 
> has been overlooked to some degree on purpose in favor of standardization.
>
> I stay out of many of these threads because the issue you guys face up North 
> are so far from the world that I know that your needs are completely 
> different and more important than the same issues here. BUT, cut grooving 
> schedule 40 here in order to keep from trapping water in a coupling or using 
> a tri-seal coupling would not gain you much down here.
>
> Greg McGahan
> Operations Manager
>
> Living Water Fire Protection
> 1160 McKenzie Road
> P.O. Box 877
> Cantonment, Florida 32533
> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> g...@livingwaterfp.com
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org 
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
> Sent: Friday, December 11, 2009 10:58 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: tri seal gaskets
>
> No invoice, no opinion? :)
>
> I don't think I'm wrong in stereotyping most sprinkler contractors as being
> a bit myopic when it comes to the big picture and our cost relative to it.
>
> Sure, most of our customers want to spend less- or nothing- on sprinklers.
> HOWEVER, when the total system cost over the life of the building is
> analyzed, upgrades may be cheaper than replacing the system or the
> interference with operations that sprinkler problems can create- and I'm not
> even addressing damage.
>
> Am I correct that a little education is all that is necessary to convince
> owners to stay the course of your upgrade, and buy peace of mind? I believe
> it costs more to LIGHT the building over its life than it does to BUILD the
> place. So while it looks like a lot when we're only looking at our pricing,
> look at the big picture and understand why we're last trade bought out.
>
> When we've suggested design changes in DB work we were quickly educated that
> while you can save a branchline per bay, the effect of a change in the steel
> was a quantum increase in comparison to the paltry $ we were saving.
>
> If your work is 1~5% of construction, we'd have to be free to overcome a
> change in building steel of only 5% of 38% of the building cost that steel
> may represents.
>
> Glc
> Ps- I made up the 38% for steel as % of total building cost. Seemed close
> enough for illustration purposes.
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Scott A.
> Futrell
> Sent: Friday, December 11, 2009 11:34 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: tri seal gaskets
>
> George,
>
> I'm not Dave or Mark, and I don't have opinions (!), but the experiences are
> bad with rusting (all the way through in less than 20 years) to freeze and
> pipe separation - without flush seal gaskets.  We spec sch. 40 with cut
> grooves, but get much negative feedback for conservative, more costly
> approach.  Btw -7°F here this morning, but now it's +7!
>
> Scott
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
> Sent: Friday, December 11, 2009 10:18 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: tri seal gaskets
>
> Before Frozen Dave became an SH wizard, he'd have chimed in here about the
> "mini-dams" that get created when roll-grooved piping has condensation
> puddling both in the pipe ends uphill from the groove intruding up into the
> bottom of the pie, as well as the water sitting in the gasket. Potential for
> corrosion and freeze/break. Not much we'll be doing about the puddling on
> the bottom of the pipe, short of using Sch40 and cutgrooving (or thread it!)
> but the area on the bottom of the coupling may be subject to a freeze/break.
>
> Since he's native North Dakota, I'll defer to his expertise and experience
> with cold far surpassing anything I'd tolerate before moving south.
>
> Mark, you're entitled to an opinion on this and have remained in the same
> tundra. Do you experience problems from liquids accumulating in these lower
> areas? I can't ask Dave now, he'd suggest clean agent or Hi-Ex.
>
> glc
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Denhardt
> Sent: Friday, December 11, 2009 9:21 AM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: tri seal gaskets
>
> Any gasket that is listed for dry pipe service may be used.  Most
> manufacture's recommend using one but the other "less expensive" gaskets
> are usually listed for dry pipe service.
>
> John
>
> John August Denhardt, P.E.
> Strickland Fire Protection Incorporated
> 5113 Berwyn Road
> College Park, Maryland 20740
> Office Telephone Number:  301-474-1136
> Mobile Telephone Number:  301-343-1457
> FIRE SPRINKLERS SAVE LIVES
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bob
> Caputo
> Sent: Tuesday, December 08, 2009 5:35 PM
> To: sprinklerforum@firesprinkler.org
> Subject: RE: tri seal gaskets
>
> Other than NFPA 13, section 6.5.3.3  "Grooved fittings, including
> gaskets
> used on dry-pipe, preaction, and deluge systems, shall be listed for dry
> pipe service"  ?
>
> -----Original Message-----
> From: sprinklerforum-boun...@firesprinkler.org
> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Robert
> Thompson
> Sent: Tuesday, December 08, 2009 1:43 PM
> To: sprinklerforum@firesprinkler.org
> Subject: tri seal gaskets
>
> Is there a code that required couplings to have tri seal gaskets in dry
> systems?
>
>
> Thank you
>  Robert  Thompson
>
>  DAKOTA
> FIRE PROTECTION
> 1710 N. Washington Street
> Grand Forks ND 58206-5327
> Phone # (701) 772-8820
> Fax # (701) 772-7932
> Email rob...@dakotafire.com
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email
> to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email
> to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: supp...@firesprinkler.org
>
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to