Scott,

We post a sign on the riser that spells out the requirements for annual
testing, it sums up 4.2.4, we tell the owner we will be happy to provide
this service, but presently none have taken us up on it.  My personal
thoughts is in the residential world antifreeze is not a good option due to
the false since of security and the likelihood that the owner won't be
proactive.

I agree with you, people need to be better educated with these systems. 

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Scott A. Futrell [mailto:[email protected]] 
Sent: Monday, December 21, 2009 1:24 PM
To: [email protected]
Subject: RE: Residential Anti-Freeze Systems

Out of curiosity:

 

How will the annual testing of the antifreeze be accomplished?  4.2.4
(2007), Before freezing weather each year, the following procedure shall
be performed:

(1)   Solution in the entire antifreeze system emptied into convenient
containers.

(2)  Solution brought to the proper specific gravity by adding
concentrated liquid as needed, or a new solution be prepared, in
accordance with 8.3.3.

(3)  System refilled with the new or remixed solution

Not to mention the sampling "...two or three times during the freezing
season..." in the Annex (4.2.4)

 

If these are, or if some of these are CPVC systems won't removing the
sprinklers in the future to facilitate antifreeze replacement be a
concern (difficulty in backing out sprinklers without breaking
fittings)?

 

What am I missing?

 

I'm working on several levels to educate AHJ's, owners, contractors,
politicians, the general public, and general contractors regarding
residential sprinkler systems and when I'm asked about antifreeze these
are the questions I pose.

 

Scott Futrell

 

(763) 425-1001 Office

(612) 759-5556 Cell

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim
Johnston
Sent: Monday, December 21, 2009 12:02 PM
To: [email protected]
Subject: Residential Anti-Freeze Sytems

 

 

 

Does anybody on the forum have experience with residential antifreeze?
We

have a community in Central Washington where sprinklers are required
period

no exception, the homes are high-end getaway homes.  Some of the clients

want antifreeze as a backup measure for freeze protection; we install

Firefighter GL from the Noble Company in these systems all the
components

are piped in conformance with NFPA methods.  We hydro the systems with
water

(AHJ makes us go 200 psi) then due a bucket test with water, we then
drain

the system and pull heads at the low points to get the remaining water
out.

We then pump the glycerin in and pull heads at the high points until the

glycerin comes out, once filled we pump the solution up to about 10 psi

above the static conditions of the water supply.

 

 

 

Does this sound appropriate?  

 

 

 

  

 

Jim Johnston, P.E.

 

Fire Protection Engineer

 

Inland Fire Protection, Inc

 

1100 Ahtanum Road

 

Yakima, WA 98903

 

Phone 509-248-4471

 

Fax 509-248-1180

 

[email protected]

 

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 

For Technical Assistance, send an email to: [email protected]

 

To Unsubscribe, send an email
to:[email protected]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to