Good morning all!

Hope everyone had a WONDERFUL Christmas.

Let's start off the week with a HIGHLY technical aircraft hangar group of 
questions that I am sure this esteemed group can adequately handle ;-)

Scenario: Group-1 Aircraft Hangar

Large Hangar - In excess of 40,000 sq.ft.
Tail Height - In excess of 28 ft.
Wing Surface Area  - In excess of 3000 sq.ft.

NFPA-409 allows a choice of three (3) protection criteria:

Criteria #1 - Foam-water deluge system with a supplementary protection system. 
(Read under wing monitor nozzles or other approved protection)
Criteria #2 - Wet Automatic sprinklers AND an automatic low-level low-expansion 
foam system.
Criteria #3 - Wet Automatic sprinklers AND an automatic low-level 
high-expansion foam system.

(Low-level meaning a minimum 2ft of depth of the foam blanket to accomodate any 
flammable/combustible liquids pool fire at the floor level.)

Question #1:
Based on these protection scheme choices am I correct in my interpretation that 
the under wing supplementary protection system is ONLY required if Criteria #1 
is chosen as the protection criteria for this hangar?

Question #2:
When utilizing Criteria #3 (High-Ex Foam), am I also correct in my 
interpretation that the foam solution requirement is the total AREA of the 
aircraft hangar x 3 cubic feet/min/square ft or 132,000 cfm (44,000 sq.ft. 
hangar)

Question #3:
When utilizing Criteria #3 (High-Ex Foam), am I also correct in my 
interpretation that the sprinkler breakdown factor of 10 cfm/gpm is calculated 
based on the TOTAL sprinkler system density and demand area requirement of .17 
/ 15000?
(.17/15000 = 2550 gpm x 10 cfm = an additional 25,500 cfm of foam solution)

Question #4:
When utilizing Criteria #3 (High-Ex Foam), am I also correct in my 
interpretation that the foam solution shrinkage factor is 1.15 x the SUM of 
Question #2 and #3 above?
(132,000 + 25,500 = 157,500 x 1.15 = 181,125 cfm total foam solution 
requirement)

Question #5:
What is the most common detection and releasing method for the hi-ex foam 
generators?

Question #6:
How is the column protection requirement normally handled with a Hi-Ex foam 
system and a wet automatic sprinkler system?

I am also providing two (2) foam-water hose reel stations at 60 gpm each for a 
duration of 20 minutes and two (2) fire pumps.

Please offer any advise or direction you may have based on your experiences 
with this particular scenario.

Thanks,

Ray Vance - SET
Chief Sales Designer
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com<blocked::blocked::blocked::blocked::blocked::blocked::blocked::blocked::blocked::blocked::outbind://37/www.waynefire.com>
407-877-5563   office
321-436-2184   mobile



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to