I would say yes as long as you take the "b" dimension from the actual head location, not where the ceiling intersects the soffit. Dewayne Martinez Design Build Fire Protection New Berlin, WI
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, January 13, 2010 10:29 AM To: [email protected] Subject: soffits along walls with sloped ceilings An owner had added soffits along the wall/ceiling similar to figure 8.6.5.1.2 (b) (NFPA 13 - 2002), except the roof is sloped greater than 2:12. Does this still apply? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)