Run it by the AHJ.  Nothing says it has to be US listed, just listed by an
organization that is acceptable to the AHJ.  With credentials of the
Norwegians provided and the test standards used I could see an AHJ going
along.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Carrol
Glimstad
Sent: Friday, January 15, 2010 10:54 AM
To: [email protected]
Subject: RE: Sidewall with a 12" throwback?

Branchline running 9" off back wall due to columns protruding into room
by 8".  I found a sidewall on Tyco's website, however, it appears to be
Norwegian, listed for some agencies that I do not recognize.   It did
offer me a glimmer of hope that perhaps there was a listed (US)
counterpart.


Carrol A. Glimstad
Fire Sprinkler Systems Designer

Cosco Fire Protection, Inc.
500 Menlo Drive, Suite 150
Rocklin, CA 95765
Ph:  916.652.1306
Fax: 916.652.1307
Email: [email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of tom
poisal
Sent: Friday, January 15, 2010 8:50 AM
To: [email protected]
Subject: Re: Sidewall with a 12" throwback?

Carrol, I don't believe such a listing exists, what is your installation
configuration?

On Thu, Jan 14, 2010 at 3:58 PM, Carrol Glimstad
<[email protected]>wrote:

> Does anyone know of a sidewall sprinkler that is listed for LH  with 
> an extended throwback?  Needs to cover at least 10 inches behind...
>
> Thanks,
>
> Carrol A. Glimstad
> Fire Sprinkler Systems Designer
>
> Cosco Fire Protection, Inc.
> 500 Menlo Drive, Suite 150
> Rocklin, CA 95765
> Ph:  916.652.1306
> Fax: 916.652.1307
> Email: [email protected]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>



--
Tom Poisal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to