Forest, If you look at the aboveground contractors' acceptance form from 13 it has a question as far back as I can remember asking about whether there is a coupon recovery procedure. I believe the meaning is kind of like for an operating room where all the tolls, sponges, bandages, etc. are identified and counted going in and coming out. The form wants to know if you have a method for making sure there are the same number of coupons as there are holes. You can count them and the number of holes, attach them at each tee, put them all together in a box and make them part of the as-builts, you could flush each section of pipe, you could send a camera down every line in the system--you just need to have a system (key word) for knowing there aren't any coupons forgotten in the pipe. Obviously in your example there was no system, an inadequate system, or just a mistake. I've never been comfortable around someone who says, "Don't worry, it's not loaded." He and I are coming from a fundamentally different mindset.
On Sat, Jan 23, 2010 at 12:31 PM, Forest Wilson <[email protected]> wrote: > It was recently discussed and agreed upon that a best practice to ensure that > cut out discs from the installation of mechanical tees should be attached to > the mechanical tee after installation for visual verification that the disc > was retrieved and the tee installed. > Now I recently drained a wet system, tree and a cutout disc came out of the > main drain. > The installing contractor did not attach the cutout discs to any mechanical > tees. > Aside from this issue, some of the drops installed were clogged near the > sprinkler. The sprinkler from a 7 ft drop could be removed and not a drop of > water would come out. > I know the owner should be notified of the observations. Should any proactive > measures be recommended regarding the cutout discs which may be in the system? > What about the clogged pipe? > Thank you. > Forest Wilson Project Manager Cherokee Fire > Protection Co. 1855 Bellbrook Ave. Ste C Xenia OH 45385 > 888-347-3079 ph 614-455-4324 fx > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Bates Technical College Tacoma, WA Member: SFPE, ASCET, NFPA, AFSA, NFSA AFAA, WSAFM _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)