7.4.4.4 is for dry systems and preaction syatems subdivided by check valves
which is under a main section 7.4 Combined Dry Pipe and Preaction Systems.
*.15.2.5.3 is Auxiliary Drains for Dry Pipe Sys. and ..... "Provision for
heat is not a requirement" see also 8.15.3.1 Protection of Piping Against
Freezing, if applicable.

On Wed, Jan 27, 2010 at 4:38 PM, Forest Wilson <[email protected]>wrote:

> 7.4.4 applies to Subdivision of systems with check valves.
> 7.4 is for combined dry pipe and pre-action systems.
> 7.4.4.4 does not apply to dry systems.
> Right? (or am I wrong?)
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Letterman,
> Todd
> Sent: Wednesday, January 27, 2010 4:17 PM
> To: [email protected]
> Subject: RE: dry system drains
>
> NFPA 13 2002   7.4.4.4  Section drain lines and dry pipe system
> auxiliary drains shall be located in heated areas or inside heated
> cabinets to enclose drain valves and auxiliary drains for each section.
> I don't know if this is what you are looking for or not. Hope it helps.
>
> Todd Letterman
> Fire Protection Engineer
> Riverside County Fire Department
> (951) 955-5273-Fax(951) 955-4886
> [email protected]
>
>
> "Life's not about waiting for the storms to pass...
> It's about learning to dance in the rain."
>
> -----Original Message-----
> From: Robert Thompson [mailto:[email protected]]
> Sent: Tuesday, January 26, 2010 12:25 PM
> To: [email protected]
> Subject: dry system drains
>
> Is there a code in 13 that states a dry pipe aux. drain or drum drip
> need to be in a heated area?
>
>
> Thank you
>  Robert  Thompson
>
>  DAKOTA
> FIRE PROTECTION
> 1710 N. Washington Street
> Grand Forks ND 58206-5327
> Phone # (701) 772-8820
> Fax # (701) 772-7932
> Email [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to