Do high-rise requirements apply to your building?
As an existing bldg, can they be waived?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, January 29, 2010 6:37 AM
To: [email protected]
Subject: Re: Retrofit Questions

Peter,

It's hard to say without specifics, but from a Code standpoint, 
existing standpipes can be used to feed a new sprinkler system. They 
will needs to be converted to wet, which means the stairwells will 
have to be heated to prevent freezing. I'm not sure where you are 
located, but the sprinkler system on each floor will probably require 
a separate control valve and flow indicator. This is required to be 
located in the stairway. Consequently, you will not be able to use 
the branches that feed the hose valves to supply sprinklers.

One issue you may have is water supply. Do you have enough water in 
the street (assuming you are on public water) to reach the 8th floor? 
This can have a big impact on design and price. My suggestion would 
be to contact a Fire Protection Engineer and get a full design done 
before you engage a contractor. They can answer that and other 
questions. That will help eliminate most of the "surprises" when 
doing a project like this. Best of luck with it. Your guests, fire 
department and insurance company will appreciate it.

Todd



At 11:36 PM 1/28/2010, you wrote:

>I am looking at an 8-story hotel that was built in 1979. It does NOT 
>have a fire sprinkler system, as it has been "grandfathered-in". We 
>are looking to retrofit a modern fire sprinkler system but due to 
>the economy, money is tight, so we are on a budget.
>
>The hotel already has 2 dry standpipes, one on each end of the hotel 
>building, it runs up through the stairwell on each floor, all the 
>way to the 8th floor. I believe it is about 8" in diameter or 
>larger. It is steel/iron.
>
>QUESTION#1 - Can this dry-pipe be used to covert it to a wet-pipe in 
>the fire sprinkler retrofit? This could save us money by utilizing 
>this pipe and making it "wet", so it carries the fire sprinkler 
>water to each floor.
>
>
>Also, the hotel has drop ceilings in all the hallways. The stairwell 
>standpipe "T's" off down each hallway, through the drop ceiling, and 
>goes to a box in the middle of the hallway, where a fire hose is located
at.
>
>QUESTION#2 - Can this dry-pipe be used in conjunction with the 
>standpipe and made to be "wet"? This pipe could then be used to "T" 
>off into each hotel room, saving costs by utilizing the existing 
>dry-pipe in the fire sprinkler retrofit.
>
>Appreciate any input....
>
>_________________________________________________________________
>Hotmail: Trusted email with Microsoft's powerful SPAM protection.
>http://clk.atdmt.com/GBL/go/196390706/direct/01/
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to