But to further the discussion there is something related that I never got logic around. I know logic and code don't always mix.
Nearly any wall, even with unrated penetrations (and maybe even uncovered openings), suffices for the purpose of not extending the protection scheme across the wall but unless it's LH or OH and has rated walls and closers (OH) you can't use room design method. Just seems odd to me we can have a small HPS with a 0.6 density next to the office and have LH in the office on the other side of the wall but when calc'ing maybe pick up LH heads on the 0.6 density depending on the size and configuration to get the 2000 sq.ft., 53.66' along the BL. But even in the LH and OH scenario you have a supply storage room in an office that is OH. Most of the time these don't have self closers on the door thus the hallway head maybe 3' from the storage head the hall is LH and the closet OH in the same calc. Yeah it doesn't matter too much in the calc's usually. It just seems odd to me we can't stop more calc's at the wall more often like we can stop the protection scheme. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Hinson, Ryan Sent: Wednesday, March 03, 2010 10:31 AM To: '[email protected]' Subject: RE: Adjacent hazards I misunderstood a superior and was looking for clarification. Thank you. Ryan Hinson Burns & McDonnell Direct: 952-656-6003 Ext 3662 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Johnson, Duane (NIH/OD/ORS) [C] Sent: Wednesday, March 03, 2010 9:58 AM To: '[email protected]' Subject: RE: Adjacent hazards If your walls extend to the bottom of the deck/ceiling, then you are physically separated and do not need to extend the higher hazard 15'. Look at that, an AHJ CAN get it right! Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 -----Original Message----- From: Hinson, Ryan [mailto:[email protected]] Sent: Wednesday, March 03, 2010 10:52 AM To: '[email protected]' Subject: Adjacent hazards NFPA 13(2010) section 11.1.2(1) states "Where areas are not physically separated by a barrier of partition capable of delaying heat from a fire in one area from fusing sprinklers in the adjacent area, the required sprinkler protection for the more demanding design basis shall extend 15 ft beyond its perimeter." The appendix gives a storage example. My question is: Is the spacing of the more demanding basis also to be extended that 15 ft for an OH scenario into a LH area through non rated walls? In other words, do I have to protect light hazard corridors or bathrooms with 130 sq ft max sprinkler spacing since they are within 15 ft of mechanical, janitor, and recycling rooms? It seems like overkill to me to have to space heads in a portion of a corridor or bathroom at 130 sq ft unless there are rated walls separating them from the other hazards. Thoughts? Thank you, Ryan L. Hinson, EIT, NICET III Fire Protection Systems Designer, Aviation and Facilities Group Minneapolis-St. Paul Office Burns & McDonnell 8201 Norman Center Drive, Suite 300 Bloomington, MN 55437 Direct: 952-656-6003 Ext 3662 Fax: 952-229-2923 www.burnsmcd.com<BLOCKED::www.burnsmcd.com> Proud to be one of FORTUNE's 100 Best Companies To Work For _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)