I know this is a very controversial issue (large 13d houses) so I am trying to 
get feedback from those who have already evaluated this type of situation.

The lowest level of this house on pilings on the beach is enclosed and lands at 
about 8,500 sq ft. It is being called a "Garage" and has a poured in place 
concrete ceiling that consists of roughly 14' x 14' bays in which the beams are 
about 14" deep - therefore it is obstructed construction.

The AHJ is asking for us to provide steel pipe and perform a 2 head 13D calc 
since he considers it no more hazardous than a normal home garage. We have not 
been awarded this contract and the bid war is still on or I would throw caution 
to the wind and say that it needs to be OH and calc accordingly. However, that 
would require a separate fire main and all that includes as the intended 2" 
Domestic line would not supply an OH calc.

My though was to do a 4 head calc and use SSU sprinklers. Would I space them at 
130 sqft or 225 sqft if I were to attempt this arrangement. Or is there any 
factual data to say that we must go to OH in this instance?

Thanks for your help.