Jay,NFPA 20 (2010) section10.8 covers this requirement as it has done in the 
comparable sections of previous editions.A fire pump has always been required 
to use it's own dedicated transfer switch where emergency power is needed.
 It sounds like this electrician is proposing to use normal power to serve the 
fire pump,which is also not allowed (see the power source section).The fire 
pump must have a dedicated/uninterrupted power source.


---- Jay White <[email protected]> wrote: 
> I know the transfer switch has to be UL listed and FM approved for fire
> pumps,  but electrician is saying the fire pump can run off building
> transfer switch. What section of NFPA says the transfer switch for fire pump
> is separate from building transfer switch?
> 