Jay,NFPA 20 (2010) section10.8 covers this requirement as it has done in the comparable sections of previous editions.A fire pump has always been required to use it's own dedicated transfer switch where emergency power is needed. It sounds like this electrician is proposing to use normal power to serve the fire pump,which is also not allowed (see the power source section).The fire pump must have a dedicated/uninterrupted power source.
---- Jay White <[email protected]> wrote: > I know the transfer switch has to be UL listed and FM approved for fire > pumps, but electrician is saying the fire pump can run off building > transfer switch. What section of NFPA says the transfer switch for fire pump > is separate from building transfer switch? > > Jay White > Estimator/Design Manager > Dynamic Fire Protection > 1807 Hwy. 25 South > Starkville, MS 39759 > Phone: 662-324-1550 > Fax: 662-324-1545 > Cell: 662-312-2426 > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)